This I don't understand. Using Table 4D5 clipped direct 4mm has capacity for 37A, 2.5mm has 27A (so using a ring 54A). Both well within the breaker capacity of 32A. So why would my option not be viable?
Why are you using the clipped direct figures when the existing cables are buried in plaster and I assume your new cables will also be buried in plaster. For 4mm² T&E buried in plaster you are looking at 26 - 27A so your lolipop fails at the start as I doubt it is all clipped direct allowing you the 37A you quote. The reference methods are there for a reason and you can't just pick the figures that suit your needs

Unless you have followed the route of the existing cabling it is likely that the skts are not in order on the ring through each room also adding skts as you go would more than likely cause more issues than it solves
 
Last edited:
Why are you using the clipped direct figures when the existing cables are buried in plaster
As I put in the original post this will be clipped direct. In reality this will be clipped direct up to the point of the 1st socket which is the only part I am doing now after which it goes to 2.5mm ring. So not picking figures that suit my needs, more what is intended to be followed

Now in future when it switches to a 4mm radial throughout the other rooms will indeed be burred in plaster at which point I would need to switch to a lower breaker
 
Also are you sure about this? Reference method C I have seen referred to as "Clipped directly to the surface / buried below the surface on a plastered wall."

Method C

  • Clipped to a wall or ceiling.
  • Buried direct in plaster.
  • SWA running down wall.

reference method explained - https://www.electriciansforums.net/threads/reference-method-explained.70017/
Maybe I read the regs differently to you
Read the notes for Table 4D5 then refer to Table 4A2 as the notes suggest and Installation Method 20 does not look like a cable is buried in plaster
 
Read the notes for Table 4D5 then refer to Table 4A2 as the notes suggest and Installation Method 20 does not look like a cable is buried in plaster

I read TABLE 4A2 Number 57

Screenshot 2022-08-04 at 15.25.15.png

Which refers to note o
Screenshot 2022-08-04 at 15.26.35.png

Which states Reference Method C
 

Reply to Temporary Hybrid/Lollipop Circuit in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
742
Currently planning a new rewire for my kitchen and want to get things right first time when it comes to appliances consumptions and circuits...
Replies
0
Views
994
Hi! Is there any way to know if I have a ring or a radial circuit in a division of the house? Thanks!
Replies
6
Views
2K
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
669
i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
295

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock