Discuss Testing questions? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Colin33
I haven't done any testing for a long time so some help with a few questions muchly appreciated please!
Firstly, earthing. The supply cable (from underground) appears to have several strands of the sheathing coated in black insulation and which is used as the neutral with the remaining bare sheathing as earthing. I've not seen this before, only the usual TNCS where the whole of the sheathing is the combined earth/neutral. Does this mean I have a TNS system? BTW, the Ze measurement is 0.16
Secondly, this is an all RCBO installation. However, when testing the trip times of all circuits generally come up with the same reading of 19ms, even on the fast trip test. There were a few minor variations when switching test between 0 & 180 degrees but 19ms was the favourite reading! I'm presuming that these particular rcbo's won't trip any faster than this?
Also, all circuits have a combined fixing method in that parts of the wiring are clipped direct to timber above the loft insulation, then drop into conduit in plastered walls and/or through insulated stud walls, and sometimes into plastic trunking and conduit in places. Which 'reference method' should one choose to put on the paperwork in this instance?
Cheers....
Cheers....
1 The cable is concentric and the earthing system is usually TN-C-S (concentric is used on TN-C-S supplies to lessen the chance of broken PEN conductors)
2 It's unusual to have such consistent tripping times but assuming confidence in your test instrument, that's what it's reading.
3 Record the worst-case reference method then you're always covered!
TNCS systems I've seen before have not had a few strands of the sheath with black insulation, that's what's confusing me. Also, there is usually a PME warning sticker put in place by the DNO but there isn't one in this case?
If I record the worst-case reference method then wouldn't questions be asked as to why I haven't applied the relevant correction factors to the circuits?
And 19mS is bloody fast, have a look at the requirements of 415.1.1
Cheers............Howard
Yes it's well within requirements, but usually get around 12ms with the regular rcd's (as opposed to these rcbo's)
This is the modern DNO cable for TN-S, it's called a ''Split Concentric cable''. It is basically the same as the TNC-S/PME concentric cable, but has, as you have stated, insulated neutral conductors (strands) and bare earthing conductors strands forming the concentric sections.
Ah, thanks for that. So it is a TNS supply rather than a TNCS then? The Ze seems rather good for a TNS supply though??
Reply to Testing questions? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Hi Everyone, Sorry for all the questions. With he help of a friend, I recently installed some insulation into my mother's loft. Whilst adding...