Darkwood

Got a callout from a mate saying his light are out and all circuits are on, also he thinks something smells funny so given the latter info I said it best I pop over and check it out, now considering I went to look at the lighting issue, what I found in the board was an example of the issues of condensation running though the breakers over the years.
The burnt out mcb was a 40amp shower supply but the heat burnt through the adjacent main switch into the live pole and a 32amp mcb on the other side, all effected breakers were rendered useless welded in the on position and taking power direct through the mainswitch regardless of its position.
All uneffected mcb's of this heat damage were stuck physically in the on position as the mechanics has siezed with the damp although the lighting did operate internally but couldn't reset.
I raided by box of spares and replaces the heat damaged devices and the lighting, disconnected temp' other circuits ready for a board change.
The cellar has a extract fan design to remove the damp air but it was never switched on.
I'll be passing this job on to a mate who can sign off the new board as I don't do domestic and I'm too busy for a guv job (which I never do ;) )

burntout 2.jpg
Burnt out.jpg
 
To be fair the issue was not the brand nor the tightness of connections that usually are a factor, it was good old H2O and I've seen this happen to the best of brands under the same conditions.. the damp penetrates the mcb, corrodes the contact points creating high resistance, it tends to show on high current circuits before low current ones if effecting multiple devices and that was exactly what happened here.
the hardest part of doing a temp' repair is getting the gear out when it rusted solid on terminations like the busbar, took alot of persuation with a ratchet set and a tapping hammer to shock them loose without reeming the heads out.
You can see in the pic that the terminals are corroded too.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
The dangers of condensation!
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5
Unsolved
--

Advert

Thread statistics

Created
Darkwood,
Last reply from
DPG,
Replies
5
Views
1,645

Advert

Back
Top