Rewiring a 60s house. Loft has 270mm of insulation. Ground floor is solid. First floor is going to have wet underfloor heating installed so will have insulation stuffed into the void. Joists are 200mm deep. Seems I will have to run a fair few cables in the first floor. Am I correct in thinking this will be reference method 101? Also, it might be possible to avoid the insulation by using the safe zone at the top of the walls. I know that's to the regs, but I worry that it isn't what Joe Blogs with his drill would expect. Damage to decoration isn't really an issue.
 
i have same problem with my customer he loves his insulation
Rewiring a 60s house. Loft has 270mm of insulation. Ground floor is solid. First floor is going to have wet underfloor heating installed so will have insulation stuffed into the void. Joists are 200mm deep. Seems I will have to run a fair few cables in the first floor. Am I correct in thinking this will be reference method 101? Also, it might be possible to avoid the insulation by using the safe zone at the top of the walls. I know that's to the regs, but I worry that it isn't what Joe Blogs with his drill would expect. Damage to decoration isn't really an issue.
 
So am I correct about the reference method?

Do other people use the "safe zone" at the top of walls?
 
It is regarded as safe as the circuit will be RCD protected.
I'm afraid I'm old school and both that method and the"V" in the wall method to me is quite inanne. How many home owners know where safe zones are, but a good majority will sort of take note that if there is a socket or switch there, there is a good chance cables might be running to it, espicially vertically.

So no the safe zone 150mm from ceiling would really be a last resort thing, but that is just IMO
 
Regulation 522.6.6 (v) 150mm of an angle formed by two adjoining walls or partions. So either side of a 'V" where the 2 walls meet.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Thermal insulation in floor void
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
6

Thread Tags

Advert

Thread statistics

Created
rryles,
Last reply from
malcolmsanford,
Replies
6
Views
2,558

Advert