sdc8843

Hi Guys,

I have just started with a new company and want to run a couple of things by you all.

1. They only want Minor Works Certs filled out for changing lights in bathrooms and sockets in kitchens. I thought it was work on any circuit in kitchen and bathroom because they are special locations.

2. On a certificate in the box Maximum Zs permitted by BS7671 they want me to record 1667 ohms for any circuit controlled by a RCD rather than the tabulated value in the regs.

What are your thoughts
 
For changing lights sockets etc in special lcation a minor works is fine as long as there is no changes to wiring.
The RCD is an interesting one i would they could possibly be right however i personnally use the tabulated values (@100%) with regards to the overcurrent device.
At the end of the day its down to whoever signs as the Inspection and Testing to decide what values they put.:confused:
 
Hi Guys,

2. On a certificate in the box Maximum Zs permitted by BS7671 they want me to record 1667 ohms for any circuit controlled by a RCD rather than the tabulated value in the regs.

What are your thoughts

This is a tabulated value in the regs. Table 41.5 p 50
 
The correct value is the tabulated value agreed
The fgure of 1667 is for an rcd on a TN system

With a TT system.the earth loop impedance is usually pretty high ,therefore the fault current used to operate the RCd will be low and it dis connects as it should
On a TNC-s system the fault current will be very large and could cause a high enough volt drop that may cause non functioning of the electronics of the RCd, and it may not operate,so cant be relied on for fault protection

Having said that,the person oversigning the certificate takes that responsibility,so just go with his method, then keep in mind why I detest the shortcomings of the Qualified supervisor system nonesense operated by that most electricial industry un friendly creatures the Niceic
 

Reply to Thoughts please in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Evening all, I just wanted to see if electrical improvers/adult trainees with appropriate levels of experience and who hold testing...
Replies
0
Views
1K
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Replies
11
Views
2K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
764
Howdy All, just after a 2nd opinion as i'm doubting myself. I went to a property to look at replacing the ccu, I noticed what I thought was a...
Replies
17
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock