Discuss Tncs again Electric gates in the The Welcome Forum area at ElectriciansForums.net
R
Rapid sp4rk
Scenario is
2.5mm swa sent out via 13amp sfs to electric gates from 16amp mcb in consumer unit as part of a tncs/pme earthing arrangement. do the gates really need bonding with 10mm or converting to TT Seems over the top any thoughts on this subject would be happily received
Just Ive come across this twice in the last 6 months I agree with you entirely I'm old school an thought this was a strange set up. Not something I would do personally but why would anyone else is my question ?
Gates on last property were max 10m from house at closest point roughly 20m from MET
only way to be sure is to test gates as to whether they are extraneous. Megger between gate and MET. if > 22 k Ohms, then no need to bond.
And provided it's got 30mA RCD, if the measurement is less than 50V/30mA = 1667 Ohms it's ok too (since a fault to the metal of the gate will cause the RCD to disconnect supply).
It's the old tncs outside again Ive personally never bothered to rod a gate post regarding electric gates on a tncs or bonded them with there own dedicated cable generally just earthed using the supply cable usually a 2.5 or 4.0mm earth back to CU was just wondering if anyone else does that Head scratching
Reply to Tncs again Electric gates in the The Welcome Forum area at ElectriciansForums.net
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Good Morning everyone. Quick question regarding a sub main from a TNCS supply feeding an outbuilding on TT. This is a domestic installation not...
Hi Ive looked around and i cant see this particular scenario being discussed. I think i may have been a numpty, but bear with me. I have just...