- Reaction score
- 3,010
Did a lot of miles today and was pondering.
This is not a real scenario.
Not necessarily "how often does a Ze make an installation impossible?" but more..
If, the measured Ze is say 0.30 Ohms and you then design your installation to keep your Zs's within BBB max allowances, does the DNO have a responsibility to maintain the measured Ze or can they simply state 0.8 Ohms.
For an example you install a 10KW shower.
At time of installation the Ze is 0.3 Ohms.
Your R1+R2 is 0.1 Ohms, Zs of Approx 0.4 Ohms.
10mm T&E on a B50 Zs limit = 0.69 Ohms.
So, job done, cert issued and notified.
Stay with me....
6 months later there's a change of tenancy and the landlord has an EICR done. I nkow
Now the Ze is 0.6 Ohms and my installed circuit is measured as 0.7 Ohms and is listed as a C2 on the cert.
What happens, will the DNO just state "0.8 Ohms not our problem"
Stay with me....