Did a lot of miles today and was pondering.

This is not a real scenario.

Not necessarily "how often does a Ze make an installation impossible?" but more..

If, the measured Ze is say 0.30 Ohms and you then design your installation to keep your Zs's within BBB max allowances, does the DNO have a responsibility to maintain the measured Ze or can they simply state 0.8 Ohms.

For an example you install a 10KW shower.

At time of installation the Ze is 0.3 Ohms.

Your R1+R2 is 0.1 Ohms, Zs of Approx 0.4 Ohms.

10mm T&E on a B50 Zs limit = 0.69 Ohms.

So, job done, cert issued and notified.

Stay with me....

6 months later there's a change of tenancy and the landlord has an EICR done. I nkow

Now the Ze is 0.6 Ohms and my installed circuit is measured as 0.7 Ohms and is listed as a C2 on the cert.

What happens, will the DNO just state "0.8 Ohms not our problem"
 
TL;DR
Changing Ze, who's responsible?
SuperlecDirect - ElectriciansForums.net Electrical Suppliers
This official sponsor may provide discounts for members
Aico 3000
Vortigern

Vortigern

Esteemed
Arms
If the Ze is within stated values as supplied by the DNO I tend to think they will not take any action. Sometimes it is possible to talk with someone and discuss that change and there would be a slim possibility they may check their earth. They are required to maintain the earth as required under ESQCR (24) but whether they would see a legal responsibility to do so in the scenario described I think is remote. And the figures you have shown suggest a change from requirements of .01 ohms so would that be a C2? But anyway the 80% rule applying would mean a significant non compliance I agree. Difficult as to how they would propose to remedy such a C2
 
Leesparkykent

Leesparkykent

Mod
Mentor
Esteemed
Arms
Supporter
Wouldn’t be a C2 as it would be RCD protected being a shower so the RCD would provide the earth fault protection. No code necessary.
 
multimick

multimick

-
Esteemed
Arms
why are we as sparks so pedantic about things,in my opinion a discrepancy of anything like 0.05 ohms is irrelevant due to all sorts of things ,different meters ,tightness of croc clips, unclean conductor connections etc etc .the dno in my experience would take no action.
 
GBDamo

GBDamo

-
Esteemed
Arms
Supporter
  • Thread Starter Thread Starter
  • #5
I knew i was asking for trouble by making the numbers so tight, schoolboy error.

Its a hypothetical scenario so imagine the change to be significant.
 
davesparks

davesparks

-
Mentor
Esteemed
Arms
I knew i was asking for trouble by making the numbers so tight, schoolboy error.

Its a hypothetical scenario so imagine the change to be significant.
If the change is significant then the DNO will do something about it.
 
GBDamo

GBDamo

-
Esteemed
Arms
Supporter
  • Thread Starter Thread Starter
  • #7
Wouldn’t be a C2 as it would be RCD protected being a shower so the RCD would provide the earth fault protection. No code necessary.
I've seen 1667 Ohms listed as max Zs on EICRs before where RCDs are present but thought it was frowned upon, relying on an RCD for fault protection.
 
Midwest

Midwest

-
Esteemed
Arms
Might be wrong, but aren’t those values given ‘typical’ values not maximum, and the DNO may or may not try and reduce them, if it exceeds the typical value.
 
R

radiohead

Esteemed
Arms
I've seen 1667 Ohms listed as max Zs on EICRs before where RCDs are present but thought it was frowned upon, relying on an RCD for fault protection.
An RCD is a permitted device for earth fault protection on a TN system, I dont have the BBB to hand for the reg number but it is (obviously) in the section on fault protection for TN systems! and clearly states the maximum Zs in the table for RCD's applies (41.5 off the top of my head ??). A lot of electricians simply dont accept it, but technically, where a 30ma RCD protects a circuit the maximum permitted Zs is 1667 ohms regardless of the earthing system.
 
Pretty Mouth

Pretty Mouth

-
Esteemed
Arms
An RCD is a permitted device for earth fault protection on a TN system, I dont have the BBB to hand for the reg number but it is (obviously) in the section on fault protection for TN systems! and clearly states the maximum Zs in the table for RCD's applies (41.5 off the top of my head ??). A lot of electricians simply dont accept it, but technically, where a 30ma RCD protects a circuit the maximum permitted Zs is 1667 ohms regardless of the earthing system.
411.4.5, 411.4.204, and table 41.5
 
davesparks

davesparks

-
Mentor
Esteemed
Arms
but technically, where a 30ma RCD protects a circuit the maximum permitted Zs is 1667 ohms regardless of the earthing system.
It is not 1667 ohms under the BBB, it is 7667 ohms. 230/0.03=7667
 
Pretty Mouth

Pretty Mouth

-
Esteemed
Arms
It is not 1667 ohms under the BBB, it is 7667 ohms. 230/0.03=7667
Half agree?
411.4.204 says "the maximum values of earth fault loop impedance in Table 41.5 MAY be applied", not MUST be.
However, I believe the calculation is (230 X 0.95)/0.03 = 7283.3.
But who cares? Never going to get close to any of these values in a healthy circuit.
 