Discuss Type of Installation in the UK Electrical Forum area at ElectriciansForums.net
Hi Guys, I would like your take on this Installation. The Supply source is in a switch room & the cable is terminated at the rear of Switch Fuse Disconnector, see photos. The intake at the Distribution Panel is also shown. You will see that the Neutral is connected to the panel metal work. The cable is glanded to the top of the same panel. Assuming the earth path is from gland to gland at either end of the cable. Without further investigation as to the earth terminations at a glance would you say this is unusual linking the neutral to earth.
What is the source of supply? Public network / on-site transformer / generator? Where is the meter relative to that ISCo neutral block?
The source of supply is TNS I think, a 1200 Amp TP & N intake supplied from Public network into Main Power Room with meter then 3TP & N sub main supply to Distribution Panel in small Switch Room. Length of cable run is around 40 Meters.
I have a ELI of 0.06 at Neutral to metalwork bond on the DB/panel.
If that cable is definitely not part of the DNO supply that neutral should not be bonded to earth. Looks like it has been there a long time, 50-60 years I should imagine.
The supply is definitely fed from the main Busbars in the old Slatter switchgear which is then distributed around the Business Park. we have 3 more Switchrooms.
The supply in question is the only one with the neutral/Earth link to the Panel.
I will now have to calculate the CSA of the Steel wire Armour of the cable to make sure it is of adequate size, as with the link removed this will be the Main Earth Conductor.
It is possible at some point that was DNO equipment judging by the bare earth and and the lug.
Reply to Type of Installation in the UK Electrical Forum area at ElectriciansForums.net
I'm working on a system that has been installed incorrectly. It's a 3ph Hager board with 8 swa cables glanded into the bottom entry panel. The...
can anyone please advise on where the wires go? My electrician installed a new cable ready for when I bought a security light. The cable as shown...
I needs to install 7 external bulkhead lights, but I could do with a steer on bringing the cable into the light - see below The glass which came...