Discuss Upgrading earthing conductor in the UK Electrical Forum area at ElectriciansForums.net
leep82
I am in the process of pricing a DB change for a customer and am a little unsure as to what to do with the earthing conductor. The system is TT and the earthing conductor looks to be 6mm, tails are 16mm with a Ze of 47.7ohms. The main protective bonding conductors have already been upgraded to 10mm, as a stair lift has recently been installed and i assume it was done at this time by whoever carried out that work. The earthing conductor is not buried but where it is terminated to the rod it is protected against corrosion. And shows no signs of thermal damage. A quick look in the regs tells me that the minimum csa that would be allowed is 4mm. As i am bringing the DB upto current regs should i do the same dor the earthing or am i creating more work for myself and cost for my customer.
If protected against corrosion and is mechanically protected you can go as low as 2.5mm in a TT so you may as well leave it.
Reply to Upgrading earthing conductor in the UK Electrical Forum area at ElectriciansForums.net
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
6K
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...