I am in the process of pricing a DB change for a customer and am a little unsure as to what to do with the earthing conductor. The system is TT and the earthing conductor looks to be 6mm, tails are 16mm with a Ze of 47.7ohms. The main protective bonding conductors have already been upgraded to 10mm, as a stair lift has recently been installed and i assume it was done at this time by whoever carried out that work. The earthing conductor is not buried but where it is terminated to the rod it is protected against corrosion. And shows no signs of thermal damage. A quick look in the regs tells me that the minimum csa that would be allowed is 4mm. As i am bringing the DB upto current regs should i do the same dor the earthing or am i creating more work for myself and cost for my customer.
 
I am in the process of pricing a DB change for a customer and am a little unsure as to what to do with the earthing conductor. The system is TT and the earthing conductor looks to be 6mm, tails are 16mm with a Ze of 47.7ohms. The main protective bonding conductors have already been upgraded to 10mm, as a stair lift has recently been installed and i assume it was done at this time by whoever carried out that work. The earthing conductor is not buried but where it is terminated to the rod it is protected against corrosion. And shows no signs of thermal damage. A quick look in the regs tells me that the minimum csa that would be allowed is 4mm. As i am bringing the DB upto current regs should i do the same dor the earthing or am i creating more work for myself and cost for my customer.
If protected against corrosion and is mechanically protected you can go as low as 2.5mm in a TT so you may as well leave it.
 
Last edited:

Reply to Upgrading earthing conductor in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
861
Hi there, Just a quick question. Does a main protective bonding conductor require UV protection when run outside? I am under the impression that...
Replies
3
Views
710
This is a question (or discussion probably) regarding selecting the main earthing conductor, and subsequently the main equipotential bonding...
Replies
26
Views
7K
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
527

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock