and just to clarify. if the existing meter tails are buried<50mm, you do not have to fit RCD to protect them. you only need to do this if you fit new tails. that's because regs. are not retrospective.


...otherwise every 2 hour job would end up taking 3 months. Unpaid.
 
Hi All

I am new to this site, and was wondering if you can guide us to the right direction, I am doing EICR's and I have come across flats which are wired from submains with 16mm2 TW&E and the cable run is about 12 meters protected by kfm 60amp switch, my question is this installation is over 20 years old and the earth from from submains 16mm TW&E is used, which is 6mm and is non compliance to current reg, my question is which code would this be classified as? C1 C2 or C3

Thanks

Adam
 
at each sub-main, measure the PEFC. then apply the adiabatic. you will find that 6mm is adequate to carry the fault current for the period of time it takes tha 60A fuse to blow ( in most cases). if so, then no code.
 
Hi All

I am new to this site, and was wondering if you can guide us to the right direction, I am doing EICR's and I have come across flats which are wired from submains with 16mm2 TW&E and the cable run is about 12 meters protected by kfm 60amp switch, my question is this installation is over 20 years old and the earth from from submains 16mm TW&E is used, which is 6mm and is non compliance to current reg, my question is which code would this be classified as? C1 C2 or C3

Thanks

Adam
I agree with the above, welcome to the forum.
Please try not to multiple post the same question.
To start a new post, from the main page, enter the appropriate forum section and click on the start new post button in the top right.
 

Reply to Upgrading meter tails and main earth for a C/U change in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi all, Customer has an extension and this compromises existing meter position, DNO is extending incomer and putting meter box on a different...
Replies
3
Views
402
Client has had a meter installed for a new consumer unit in their shop they are looking to rent out the spare space for a barber shop so they want...
Replies
10
Views
311
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
827
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
890

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock