Discuss Use RCD as on/off switch in the UK Electrical Forum area at ElectriciansForums.net
Is it permissible to use the reset + test buttons of an RCD plug adapter as on/off buttons for a 10A load?
I have a 2000W power saw which I want to switch on and off at the socket under load, ie. the tool's own switch will be permanently on. (The details are un-important.)
I have an extension cable with unswitched sockets, and want to use an RCD for safety. I don't really want to add a third component in the form of a switched multi socket adapter, and in any case like the idea of quick, colour-coded push-buttons to operate the saw.
Are the reset & test buttons suitable for such load switching?
No as they are designed as test switches and not for functional switching. They would fail eventually, probably quite quickly with a 10 amp load.
As above, a 2kW power saw will have a high inrush current so it will quickly burn the RCD contacts out.
Ideally you are looking for a "Direct On Line" starter such as this:
https://uk.rs-online.com/web/p/dol-star-delta-starters/9094079/
Most 3-phase starters can be wired for single phase, they are basically a 3-pole contactor and start/stop buttons to allow the windings of the contactor the be energised and de-energised. Also they release automatically on power fail, so it the mains returns after a fault the motor does not burst in to life!
Also if you are bying a "3 phase" starter it has to be rated at 6kW or more for your 2kW motor as they give the rating when running on 3-phase.
change the extension lead for one with switched outlets. if a switch on that fails, it's a cheap replacement.
The good thing about an NVR is they switch off automatically if you get a power failure, in as a trip of the MCB or RCD, so when you switch the power back on the unit does not start up by itself, you have to reset the switch, I have them on all my large workshop tools, even the extractor.
Reply to Use RCD as on/off switch in the UK Electrical Forum area at ElectriciansForums.net
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Im making this cct for fun. Ive seen it in a video on youtube, with different IC's. So I decided to adapt the cct to what IC's I already have. And...
Hi I know I have to do more testing but I just want to see if there is something I’m missing. Customer said light fitting in the loft was...