Greetings.
Let's say you have a 2.5mm cable that you want to extend by quite a long run.
After looking at your load and volt drop calculations you arrive at a cable size for the extension of 6mm.
Would it be bad practice to add a 6mm extension to the end of a 2.5mm cable?
The circuit protection would be calculated to protect the 2.5mm cable IE a 20 Amp circuit breaker, the only reason to use the 6mm cable is simply for volt drop issues.
It is not possible to lay a new cable from the board, this is the only option.
I can't see anything in the regulations to say this is wrong but I was wondering what people thought about this.
Thanks.
Let's say you have a 2.5mm cable that you want to extend by quite a long run.
After looking at your load and volt drop calculations you arrive at a cable size for the extension of 6mm.
Would it be bad practice to add a 6mm extension to the end of a 2.5mm cable?
The circuit protection would be calculated to protect the 2.5mm cable IE a 20 Amp circuit breaker, the only reason to use the 6mm cable is simply for volt drop issues.
It is not possible to lay a new cable from the board, this is the only option.
I can't see anything in the regulations to say this is wrong but I was wondering what people thought about this.