DURING THE COURSE OF AN INSPECTION ONE OF THE SINGLE PHASE RADIALS supplying an item of fixed equipment is to be checked for volt drop.

45A full load, 80m length, 10mm singles,70 degree thermo singles, steel conduit, mohms/m at 20 degrees=1.83(p166 OSG)

Apparently this is a closed exam. How can this be calculated without reference to the tables??
:confused:
 
This is a 2391 question

DURING THE COURSE OF AN INSPECTION ONE OF THE SINGLE PHASE RADIALS supplying an item of fixed equipment is to be checked for volt drop.

45A full load, 80m length, 10mm singles,70 degree thermo singles, steel conduit, mohms/m at 20 degrees=1.83(p166 OSG)

Apparently this is a closed exam. How can this be calculated without reference to the tables??
:confused:

You wouldn't need reference to the tables as all info has been provided.

To get VD the calculation would be (mΩ/m x 1.2 x 2) x Ib x L ÷ 1000:

(1.83 x 1.2 x 2) x 45 x 80 ÷ 1000 = 15.8V (6.9%)

You multiply the conductor resistance by 1.2 to correct it for 70°C, then multiply by 2 to include the neutral.

Now multiply by 45A and then by 80m and divide by 1000.

This is how the values in the VD tables are worked out (mΩ/m x 1.2 x 2 = mV/A/m). Remember that and you won't go far wrong. ;)



Calculation from the VD tables is mV/A/m x Ib x L ÷ 1000:

4.4 x 45 x 80 ÷ 1000 = 15.8V (6.9%)

This is no good as it's over 11.5V (5%)
 
Last edited by a moderator:

Reply to Volt Drop in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hello, New trainee electrician so sorry if this is a dumb question I feel confident with calculating the volt drop for a ring and radial circuit...
Replies
2
Views
2K
all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
729
Hi! Once you've calculated the voltage drop in Volts - you divide by 400V for three phase right? For example: three phase 30kW appliance, 10mm...
Replies
5
Views
2K
I am trying to understand 3 phase volt drop. I understand single phase VD. Lets say we have a 70 meter run of 35mm, 5 core cable from the supply...
Replies
6
Views
2K
Morning team Question about volt drop. I presume I am missing something here. So firstly the facts out the OSG. Table 7.1, page 66, lighting...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock