Discuss What is the longest cable run u have done in meters for a sunnyboy1200 the main bord? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

B

bob2041

-What is the longest cable run u have done from the sunnyboy1200 to the main fuse board, its says max cable 2.5mm2 no longer then 30 metres. What happens if go 25 metres to a 30amp junction box and from the junction box put 4mm2 cable running 30 meters to the main fuse board. How would this fair out ?

I ran the cable when i had the soladin 600 ,then i got the sunny boy a year later and manual is more strict with only 30 meter cable run max.
 
Last edited by a moderator:
Re: What is the longest cable run u have done in meters for a sunnyboy1200 the main b

The a.c. cable connecting the inverter(s) to the consumer unit should be sized to minimise voltage drop. A 1% drop or less is recommended. However in larger installations this may not be practicable or economic due to the very large size of cable resulting. In this case the designer should minimise voltage drop as far as possible and must remain within voltage drop limits as prescribed by BS 7671.
[FONT=Calibri,Calibri][FONT=Calibri,Calibri]Note: the requirement for a 1% voltage drop is due to two reasons: firstly when generating, the voltage at the inverter terminals is higher than the voltage at the suppliers cutout – during periods of high power output this voltage drop must be kept to a minimum in order to prevent the inverter nuisance tripping on over voltage ; secondly the requirement ensures losses from the PV system are minimised.
[/FONT][/FONT]DTI GUIDE
 
Re: What is the longest cable run u have done in meters for a sunnyboy1200 the main b

The a.c. cable connecting the inverter(s) to the consumer unit should be sized to minimise voltage drop. A 1% drop or less is recommended. However in larger installations this may not be practicable or economic due to the very large size of cable resulting. In this case the designer should minimise voltage drop as far as possible and must remain within voltage drop limits as prescribed by BS 7671.
Note: the requirement for a 1% voltage drop is due to two reasons: firstly when generating, the voltage at the inverter terminals is higher than the voltage at the suppliers cutout – during periods of high power output this voltage drop must be kept to a minimum in order to prevent the inverter nuisance tripping on over voltage ; secondly the requirement ensures losses from the PV system are minimised.
DTI GUIDE

OK... thanks.. looks like i'll have to buy more cable yet again...
 

Reply to What is the longest cable run u have done in meters for a sunnyboy1200 the main bord? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello. Just a lowly homeowner here who is beginning to panic after a major house renovation regarding relocation of the main supply cable to the...
Replies
3
Views
2K
1990s home. 100 amp main feed. Nevada. 15 years mechanical experience on cars + motorcycles. Previous electric exp: I ran the other 50 amp 4-wire...
Replies
1
Views
890
Hello, I live in Mexico, where I have a small, un-official trailer park on my property. The property is serviced by my privately owned, 650amp...
Replies
9
Views
1K
Was wondering if the gurus can critique and/or provide recommendations on my plan to install two sub-panels in a (50'x100') 5,000 sq ft steel...
Replies
2
Views
1K
Hi, I just had a new 18th gen with surge protection installed. They disconnected the old cable and did a new run, the cert says 10 gauge was used...
Replies
24
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock