egginyourface

The other week i got a call from a little granny who had a leak in the loft which caused some of the lights to trip out and sockets etc.

I went there and isolated the affected circuits. I said i would go back in a week after everythings dried out and recconnect.

Any way, i though i would do a little zs on some of the sockets. Results i was getting was 2.19 ohms.

So i did a Ze test at origin and found just over 2 ohms. Checked main incomer and found there was no earth coming from the head.

We called eon and when they came round to have a look they told us that it wasnt there problem and it was up to the electrician to supply earth via earth rod.

The property is not in a rural area its on a normal street.

The board is 16th edition board, so was thinkng i would put a couple of rcbos in for lighting and sockets and stick an earth rod in.

Is this ok, would i need to put an rcd before the fuse board??
 
yep...all sounds familiar does this one....leigh n I had the same sort of verbal diarrhea from some stupid bint on the end of the phone just the other week.....and she didn`t stop there either....went on to intimidate the customer n all.....thing is though ..DNOs have a responsibility to maintain a reliable, stable earth for THEIR apperatus.....the fact that they will allow it to be used for a means of earthing a consumers installation could be taken as goodwill....or something like that.....but the way they behave when they just dont want to see to something is abominable.....like this scenareo we had where i pointed out to the DNO opprative that the blanks were missing on the cutout and the fact that the CUTOUT (DNO property) had no means of earthing......."not our responsibility"!! he snapped....oh yes it is pal....i thought......bloody pain they are......leigh`s had loads of nonsense with em....
 
yep...all sounds familiar does this one....leigh n I had the same sort of verbal diarrhea from some stupid bint on the end of the phone just the other week.....and she didn`t stop there either....went on to intimidate the customer n all.....thing is though ..DNOs have a responsibility to maintain a reliable, stable earth for THEIR apperatus.....the fact that they will allow it to be used for a means of earthing a consumers installation could be taken as goodwill....or something like that.....but the way they behave when they just dont want to see to something is abominable.....like this scenareo we had where i pointed out to the DNO opprative that the blanks were missing on the cutout and the fact that the CUTOUT (DNO property) had no means of earthing......."not our responsibility"!! he snapped....oh yes it is pal....i thought......bloody pain they are......leigh`s had loads of nonsense with em....

I didn't say it (for fear of being laughed at for being a mere trainee DI if I'm honest) but I thought it was the DNO responsibility to provide the earth for their kit (ie: before the fuse)
 
I didn't say it (for fear of being laughed at for being a mere trainee DI if I'm honest) but I thought it was the DNO responsibility to provide the earth for their kit (ie: before the fuse)
It's their responsibility to maintain an earth facility if they have provided one mate
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
What should i do with this one?
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
23
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
egginyourface,
Last reply from
trev,
Replies
23
Views
2,094

Advert