Hi All i know its late friday, but try and help me out with this one if you can.
Just got in now from work on the way home a landlord called me to ask if i could test a communal DB he has at an HMO.
I decided to have a look on the way home, long story short each flat was feed from this DB including the communal circuits(lights,sockets).
so i checked Zdb to each flat which was ok but when i did R1+R2 test on the supply cable to each flat i got nothing,tried to each flat and 4 out of the 5 came back with a zero reading.
Distribution board was contactum,each flat was feed from a 40 amp b type mcb (No RCD on DB).

Any thoughts as its got me wondering, the Zdb to each flat was ok but R1+R2 no reading at all.

Alright Delboy :D

Interesting thread btw.

Having re-read your opening post, I can only surmise that R2 for the sub main is broken for 4 of the 5 flats. As others have pointed out you may very well still get a cracking Zdb via parallel paths (spesh if Bonding in place for water service in each flat for example and this runs via pipework back to DB1 - the origin board so-to-speak).

So Mr R2 test will reveal all. Hopefully.
 
open switch isolater... i know
 
  • Like
Reactions: 1 person
Can't be that simple?

OP is going to be aware of any switch isolators as he'd have to be closing then to get his Zdb
 
Hawk 81 bang on with this, mcb's are open and there for no line to flat, link out from breaker output to earth bar on each individually
 
  • Like
Reactions: 1 person
Don't mean to deflate anyone, but it's hard to say really without actually being there !

Let us know Delboy
 
Are you sure the circuits are labeled correctly???

i.e you linked r1+r2 at DB circuit labeled flat1, testing at flat 1 but the r1+r2 circuit is actually flat 4?
 
  • Like
Reactions: 2 people
Are you sure the circuits are labeled correctly???

i.e you linked r1+r2 at DB circuit labeled flat1, testing at flat 1 but the r1+r2 circuit is actually flat 4?

Ohhhh thats good, didnt think of that. Nice one
 
Perhaps it needs another shilling in the meter :) or he found his mojo....
 
Last edited by a moderator:
I have returned to the thread chaps sorry about the long time away,I should have updated this ages ago apologies all round.
Right long story short went back a few days later, long wandering extension lead in hand, found out it was exactly what VMAN suggested the D.B was incorrectly labelled apart from flat 5, so when I thought I was doing r1+r2 on flat 1 it was actually flat 3 as labelled on the board.
thanks to everyone who posted for your help and suggestions
nice on lads
(don't worry in future I will report back straight away)
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Zdb ok but no R1 + R2
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
36

Thread Tags

Tags Tags
None

Advert

Thread statistics

Created
Delboy10,
Last reply from
Delboy10,
Replies
36
Views
4,584

Advert