Hi peeps

I have been asked to test a 'continuous' 20KVA UPS system. Which means the supply goes through the UPS first, and in effect with loss of power you will have changeover instantly.

The consultant has suggested to just get the dead readings, and calculate. Whilst I am happy doing this, I wonder what his reasons are?

Will the UPS throw the live readings out?

Would there be 'sensitive' fuses inside the UPS kit that might blow?
 
We never take zs readings downstream of a UPS as they have high earth leakage and will give you false readings.

If possible, and the system has an external maintenance bypass switch, try and arrange a time this can be operated as it will bypass the UPS without loss of power to the load and then you can take your zs readings.
 
Yes agree with above you get false readings with ups involved found out the hard way few years back couldn't work it out till some old maintenance spark explained to me
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Zs Readings from a 20KVA UPS system
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
3

Thread Tags

Advert

Thread statistics

Created
Guest 004,
Last reply from
Farmelectrics,
Replies
3
Views
5,643

Advert