Leesparkykent



went to a customer of mine today, she has just has a new boiler fitted. she phoned me as wasn't happy with the wiring the plumber had done connecting new boiler, programmer and wireless thermostat receiver to the existing y-plan wiring centre
he had also added the fused spur below the boiler as original heating system was plugged in to a switched socket.
what an absolute mess cables were clipped like washing lines across airing cupboard, cpc used as satisfied in cylinder stat , cpc used as ch on in programmer nothing sleeved up either to make it worse , 13 amp fuse in switched spur, existing 2.5 meb to gas and linked of this with a bit of 4mm to water. needless to say I ripped the lot out started from scratch and run in the new 10mm meb to gas and water and to top it off look at his gas pipe for the new boiler straight in front of the 2gang socket in the kitchen. The plumber had also issued a niceic domestic installer MWC for the work he done!!! looks like this scam will give any 1 a membership.
 
did she have the boiler fitted under a eco grant system ??????
 
no she is paying for it, luckily she has only paid the deposit and hasn't settled him up yet. he was reluctant to come back as was saying that's nothing wrong with it. he is going to come back and move the gas pipe (if he wants the rest of his money) and shes going to deduct 300 notes as the cost of having me out to correct his wiring lol
 
  • Like
Reactions: 1 person
Did you cost 300 to install the wall socket? Why install it behind the pipe when space is at the side of the pipe? I think you cause trouble for customer making difficult to use the socket.
 
  • Like
Reactions: 3 people
Did you cost 300 to install the wall socket? Why install it behind the pipe when space is at the side of the pipe? I think you cause trouble for customer making difficult to use the socket.

Re-read this thread......
 
  • Like
Reactions: 3 people
If that's a gas pipe then it certainly does not comply with gas regulations ( law) so a quick call to gas safe will drop him in some rightly deserved excitement
 
Did you cost 300 to install the wall socket? Why install it behind the pipe when space is at the side of the pipe? I think you cause trouble for customer making difficult to use the socket.

Ha ha r u for real. He must have put the pipe in after
 
Too true say an idiot gas fitter running gas line straight through a warm air duct.
 
Gas pipes need to be min of 50mm away. Thats plumbers for you. He should be with a scheme like NIC and that would never happen.
 
Gas pipes need to be min of 50mm away. Thats plumbers for you. He should be with a scheme like NIC and that would never happen.


if gas schemes are like electrical schemes then i doubt it.. aslong as you line their pockets your in
 
Gas pipes need to be min of 50mm away. Thats plumbers for you. He should be with a scheme like NIC and that would never happen.

50mm?

That's the separation required between pipes and cables

The separation required between pipes and sockets is different.
 
Gas pipes need to be min of 50mm away. Thats plumbers for you. He should be with a scheme like NIC and that would never happen.

50mm away from what? NIC now your having a giraffe.. If NIC did gas I would be a gas fitter for a few quid donation to their fund
 
There is a cable behind that socket hole is'nt there? No difference in my book.

You're book doesn't matter, the gas rules make a differentiation between sockets and cables.

50mm from cables and if my memory serves correctly it must be 100mm from sockets
 
50mm away from what? NIC now your having a giraffe.. If NIC did gas I would be a gas fitter for a few quid donation to their fund

I believe the people who own NIC do have a lathe finger in the pie with Gassafe
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
this really puts the plum in plumber.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
52

Advert

Thread statistics

Created
Leesparkykent,
Last reply from
Paul.M,
Replies
52
Views
5,494

Advert