- Reaction score
- 7,777
what would you put on test sheet r1+r2 no earths
Discuss no earth on lighting r1+r2 what do you put on sheet in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Yeah I take no cpc, but you have a point. Not clear is it.Is not very clear now I have reread it, is he saying there are no cpcs or no earth continuity.
No I immediately assumed no continuity till I read your post. Can you clarify please OP.Yeah I take no cpc, but you have a point. Not clear is it.
OP does the cable have a cpc?hi on testing on earths what would you put on test sheet eicr
We will get there on the end!OP does the cable have a cpc?
Are there cpcs from the dist board and none at accessories or a total absence of them?no not one. sorry this for lighting cable only
Okay you can not test for the obvious, this is a EICR, I would give it a code3 at least, if metal accessories etc code2.no not one. sorry this for lighting cable only
Right okay on the schedule it will be NA because you can't give a reading if there is no conductor to give a reading for, even though NA is self explanatory the schedule should explain this. See Daves post for Coding recommendations, light switch back boxes also need earthing unless they are plastic or have nylon fixing points.none at cu and none at the accessories
See Post 12 on this thread.just one on question which dave has coding recommendations
if you refer to switch boxes, they were not exposed and the plate fixing screws were either plastic or the back box had nylon screw lugs.what about metal back boxes
agreed.if no plastic lugs on. no cpc then it is a code 2
Personally I'd put a c2 code on the EICR as I'd class no cpc as a potentially dangerous situation although there's no immediate risk they certainly could be. let's face it who's going to argue with you. If it's not safe it's not safethanks. I got their in the end
I'd put the c2 code on your Observations sheet and put Lim in all the boxes regarding test results sheet. Also if you want put an operatonal limitation on your Observations sheet explaing why no tests have been carried out on the circuits in question.Personally I'd put a c2 code on the EICR as I'd class no cpc as a potentially dangerous situation although there's no immediate risk they certainly could be. let's face it who's going to argue with you. If it's not safe it's not safe
How is it a Limitation when the conductor is not present to do the reading in the first place. It is Not Applicable. Is it not like putting the absence of rcd testing as a Limitation because none Exist?I'd put the c2 code on your Observations sheet and put Lim in all the boxes regarding test results sheet. Also if you want put an operatonal limitation on your Observations sheet explaing why no tests have been carried out on the circuits in question.
Most people on here share the opinion that if there are no accessories which require an earth then Code 3, if there are unearthed Class 1 accessories then Code 2 as fault protection is not provided. This must be your decision though, some people feel Code 2 regardless of the current situation due to the fact that in the future an unknowing person may fit a Class1 fitting or accessory to the system no matter how many notices you stick on the CU.westward 10 the man. you said about that daves code recommendation on ecir point me in the write direction please
You would hope so but while people can go to B&Q and buy all sorts of bits the risk will always be there.I like this answer, as on the day of the test it is what you find. Just like the MOT test.
Reguarding the future modifications is that not down to the suitably qualified Electrician carrying out the work refusing to modify the circuit if it does not comply to the current version of BS7671.
Problem with those diy fittings is that they do not consider more than one cable connection, they assume just one cable dangling from the ceiling.If the cpc is present you still cant guarantee the B&Q customer will connect that right
Yes I would Code 2 an unearthed metal back box unless it had insulating nylon lugs.I see your point regarding the limitations, in regards to what code it should be dose it not matter about your un erthed back box & lid screws that someone could come in to contact with regardless of if your light switches are class 2.
I don't mean to be offensive but are you buzzing Mr Lightyear. I am struggling to have a clue what you are commenting on.ok lets get this write .no cpc in back box and pvc fronts just twin no earth a nob head takes it off
changes the front with a metal switch. fault on the switch
he take it off. he path to earth. that's why the cpc are their for savy
Or you could fit a plastic patters.Yes I would Code 2 an unearthed metal back box unless it had insulating nylon lugs.
Reply to no earth on lighting r1+r2 what do you put on sheet in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net