Discuss testing existing installations to current edition of BS 7671 in the UK Electrical Forum area at ElectriciansForums.net
The problem here, is that the current Regulations state in the introduction:
"Existing installations that have been installed in accordance with earlier editions of the Regulations may not comply with this edition in every respect. This does not necessarily mean that they are unsafe for continued use or require upgrading."
Code C1: Danger present. Risk of injury. Immediate remedial action required.
Code C2: Potentially dangerous - urgent remedial action required.
Code C3: Improvement recommended.
Either a code C1 or C2 would indicate that an installation is unsafe for continued use.
A code C3 would indicate that an installation is not unsafe for continued use, but improvement would increase safety.
Take for instance a 3 bed semi with front and rear gardens with an electrical installation designed and constructed to the 16th edition.
It has a split board with 3 circuits protected by a single RCD, all the other circuits are unprotected.
The 3 protected circuits are downstairs sockets, kitchen sockets and the cooker.
The unprotected circuits are boiler, shower, downstairs lighting and upstairs lighting.
The 3 protected circuits are fine, they comply with both the 16th and the 17th editions.
The unprotected circuits however only comply with the 16th.
There are two circuits (shower and upstairs lighting)which serve a location containing a bath or shower, both would require RCD protection to comply with the 17th.
All of the unprotected circuits may also not comply with the 17th, if any of the cables are concealed in walls at a depth less than 50mm.
The unprotected circuits are 'Potentially dangerous' or unsafe for continued use, which suggests a code C2 should be applied.
However the introduction states that because the installation complied with the Regulations ate the time of construction, they are not necessarily unsafe for continued use, which would indicate we should use a code C3.
Some will say that the phrase 'not necessarily unsafe' does not mean safe.
They are entitled to their opinion, but that is not the opinion of the IET.
The 17th edition was introduced on the 1st of January 2008 and came into effect on the 1st of July 2008.
During those 6 months, they allowed for installations to be designed to the 16th edition.
If the IET believed the 16th edition to be unsafe, they would not have allowed installations to be designed to the 16th for those 6 months.
I note that the BPG linked by Murdoch suggests a C3 code for sockets without RCD protection and a C2 for those likely to be used for portable/mobile equipment outside, or o/s zones in special location?
I forgot what the argument was about now. Gives a hand down here Maureen! Now you gave me a tenner. :)
Yes socket-outlets do appear to confuse many people.
The BPG advises a code C3 for socket-outlets that do not comply with the requirements of the 17th edition, but C2 for those that do not comply with the requirements of the 16th edition.
Which edition of the Regulations are we using when conducting the I&T?
No it doesn't make reference to the editions, why should it, why would it matter?
Anyone who has read the current Regulations will know there is no requirement for socket-outlets to be provided with RCD protection in case they may be used to supply portable/mobile equipment outdoors.
Me thinks you need to review post 56 where you clearly appear to be quoting the BPG.
Hmmm, if I were quoting something, there would be quotation marks, or some other indication that something is being quoted.
Then again you are obviously aware that it is not a quote.
I think what you need to do, is stop looking for hidden meanings in things, and just accept them at face value.
I also think, rather than just increasing your post count with these puerile posts, you should actually make a point, assuming you have one to make.
Best Practice Guide, published by the Electrical Safety Council, which I believe may be now known as Electrical Safety First or something similar.
What Westwood has not mentioned, is that all of the registration bodies in the U.K. advise their members to use the BPGs for guidance.
And what you have not mentioned is that electrical safety first or whatever they are now are funded by Certsure who own the NICEIC and ELECSA brands. So it's all the same organisation churning out this stuff.
These are the people who invented the idea that a sticker and a new CU is an acceptable alternative to installing a cpc for a lighting circuit which doesn't have one. And that at a time when the regulations specifically forbade such reliance on an RCD.
Wish I could treble like that Dave.
Yes well, I was aware that the ESC was just the NICEIC by another name.
Was not aware they also own Certsure.
Was aware that the NICEIC had taken over the ECA, ELECSA and SELECT.
Not aware that the Regulations have ever prohibited the use of an RCD to provide earth fault protection.
My understanding, is that the advice given is to provide a sticker, RCD protection and class II fittings and accessories. That the advice only applies to situations where the intention is to replace a CU in an an installation where lighting circuits do not have a CPC, and for whatever reason there is no intention to install a CPC.
No, Certsure own the NIC etc along with gas-safe aswell as far as I know.
It was the 16th edition which specifically prohibited the use of an RCD on its own in such a situation.
The advice is that it is a last resort option when faced with an absolute refusal to have the necessary work carried out. But it has become the default response in the situation you describe whenever there is no intention to have the cpc installed, often that is no intention because it is more profitable to just change CUs
Still not aware that the 16th edition prohibited the use of an RCD for earth fault protection?
Makes me wonder what the 16th expected to be done where the earthing system was TT?
Not sure what the stuff about the BPG is in relation to?
Yes, there are people out there who will change CUs at the drop of a hat whether they need changing or not.
It appears that to some, changing a CU will sort just about everything out, except of course when it doesn't.
I recall seeing a PIR which recommended replacing a CU because the current CU had no warning labels and no circuit descriptions.
The same PIR managed to identify all of the circuits except the boiler circuit, recommended further investigation to determine what the circuit was for.
My point is to explain where in the BPG it references socket outlets installed to the 16th or 17th Editions, I have just downloaded a pdf of this publication and after perusing it for some time I have no idea what you are getting at. What do I need to accept at face value. You appear to be digging a deep hole at the moment.
Ok, please explain.
I haven't looked at a BPG for a number of years, so it may be that things have changed.
However I would expect that some reference is made to the introduction in BS7671 where it states installations which complied with earlier editions are not necessarily unsafe.
I would further expect there to be a reference to only making observations which relate to particular Regulations, not to personal opinion or considered best practice.
There should also be some mention of only making observations for dangerous or potentially dangerous conditions.
You've downloaded a copy, read it, then try to explain why codes for certain situations have been chosen.
You haven't looked at it for a number of years but post 56 indicates you have and put your own spin on it. This post is clearly misleading and being a Trusted Advisor I think it should be removed.
Not sure what it is you think is being said here?
If you read post 56, it is a reply to a quoted post.
It is not a quote from the BPG.
Why you think it is misleading, I have no idea?
As for being a trusted advisor, I have no idea what you think that particular badge signifies?
#56, " The BPG advises a Code 3 for socket outlets which do not comply with the requirements of the 17th Edition............. etc.
This is what I read and I am not saying anymore, you clearly like to get a rise out of people I have seen it before I shall leave you to your Guide book.
As you well know, that was a response to this:
Stop wasting my time with these sensless and puerile posts.
I remember that character! Harry Enfield, great stuff :)
Not sure if this is the right place for this.
If you get called in for a minor residential repair and you find that the electrical installation is a mess to the point of it puting the residents at ris..........what do you do? What must you do? Surely not just walk away?
You should bring your findings to the attention of the owner. If the installation is unsuitable to take new work, then don't do it. Put your findings in writing to the customer. If the work is a repair, it may still be appropriate to carry out that repair.
In this case the customer is the landlord, not the resident, and is unwilling to have (pay for) the remedial work to make the installatiion safe.
So what next steps can be taken?
Having seen the unsafe installion, don't you have a duty to report it?
You can produce a danger notice and ( try to) get the landlord to sign, which acknowledges receipt. The tenants should report concern about the condition of the installation to the local council. If they are on their game, they can force the l/lord to carry out essential repairs. Beyond this, your hands are tied.
I often find with landlords/landladies that putting it in writing focuses minds. After all they can't claim not to be aware of the dangers then.
Reply to testing existing installations to current edition of BS 7671 in the UK Electrical Forum area at ElectriciansForums.net
Hi all, I am an electrician working for a OEM machinery manufacturer based in Germany, we are the local hub that is now taking over the...
Morning all, We are looking at qualification requirements for inspection and testing to BS EN 60204, all of our work is past the main isolator of...
I'm planning a replacement for my existing domestic CU and would like to have it sanity checked before I get an electrician involved. The main...
4K
Hi everyone, I'm currently working towards getting qualified as an electrician and am hoping to get my foot in the door with an apprenticeship or...