Update have tested all n-e using multi meter no shorts found one of the 32amp ring circuits had come away from the mcb not physically visible but have now reconnected.

Seeing that was on rcd side hoping it was that just waiting for the 40amp mcb to come back as friend took it away yesterday, then hopefully will all be up and working as Can find no faults on circuit all neutrals are on correct side aseell.

20171207_095616.jpg
 
The circuit/s need a 500V DC Insulation Resistance test, which your multimeter cannot do. Likewise, the MM cannot test the RCD. For your own sake, please get a spark to sort this out, using the correct equipment (a multifunction tester) else if there is a fire at a later stage, the insurance cover may be compromised.
 
Problem is now fixed the live off 32amp mcb was obviously causing the circuit to trip as resistance check wasn' connecting thanks to everyone who has helped and I tested n-e with multi meter with no shorts anywhere so rechrckef lives to find one had snapped

Makes absolutely no sense, but go you! Well done in making your friends installation potentially unsafe.
 
It's only a shower... Can't do much harm...

Seriously though mate, get a spark in to test. For the sake of £60 or thereabouts you are running a risk IMO. The thread to me is incoherent at times, and some good advice has been offered. I would not have a clue about ECU faults, similarly you are lacking electrical knowledge. Not having a dig, just stating a fact.
 
Problem is now fixed the live off 32amp mcb was obviously causing the circuit to trip as resistance check wasn' connecting thanks to everyone who has helped and I tested n-e with multi meter with no shorts anywhere so rechrckef lives to find one had snapped

Good that it is working, but I don't quite understand the above - where and what was the actual fault?
 
The fault seemed to be the live off one of ring mains had broken so instead of having the full circuit it was only fed one way the minute I exterminated that it stopped the tripping.

Also the breaker is slightly different size but exactly the same as the others on the buzz bar I tested the circuit as previusly said by others to check for n-e short which didn' show anything.

As for why it kept tripping before is because the water valve on the shower was flow controlled and was round the wrong way so poor flow was overheating the shower and causing it to trip.

Other than the broken live on ring main there was no other faults I could find I have spoken to a friend who's gonna do a test on it soon thanks to the people that helped and inwomt be returning here as people are not overall friendly.

20171207_102344.jpg
 
Problem is now fixed the live off 32amp mcb was obviously causing the circuit to trip as resistance check wasn' connecting thanks to everyone who has helped and I tested n-e with multi meter with no shorts anywhere so rechrckef lives to find one had snapped
A high resistance connection will not cause an RCD to trip and a multimeter will not output sufficient voltage to show up most faults.
Good luck with your continuing electrical career.
 
A high resistance connection will not cause an RCD to trip and a multimeter will not output sufficient voltage to show up most faults.
Good luck with your continuing electrical career.
Well it's fixed I redone earths as Well as I think 1 had come out and exterminated all the neutrals I was going to tidy box up but left as it was as it was signed off like it before.

Things are all connected correctly it's not like ive added it to a non protected rcd circuit so a loose connection could have been there asWell, i haven't dangerously bypassed anything or added to a non rcd side like some cowboys would do it's all connected as should be and not tripping.

Also like I said yesterday when wired to a light bulb it also tripped so wasn't tripping under load even with shower was the same after doing fuse box today tested with light bulb and didn't trip fault is fixed not bodged or covered up.
 
Last edited:
Well it's fixed I redone earths as Well as I think 1 had come out and exterminated all the neutrals I was going to tidy box up but left as it was as it was signed off like it before.

Things are all connected correctly it's not like ive added it to a non protected rcd circuit so a loose connection could have been there asWell, i haven't dangerously bypassed anything or added to a non rcd side like some cowboys would do it's all connected as should be and not tripping.

Also like I said yesterday when wired to a light bulb it also tripped so wasn't tripping under load even with shower was the same after doing fuse box today tested with light bulb and didn't trip fault is fixed not bodged or covered up.

Are you a dalek?
 
Are you a dalek?
Lmfao meant to say re-terminated that' Samsung auto correct for you and the fuse box is also being changed soon in the house as it's a plastic one.
Due to current regs with the 3 yearly check I am aware that being under the stairs that they now have to be metal and non combustible with current regs.

Will have to post a pic of my consumer unit in the property I rent you will all comment on that
 
Are you a dalek?
Its not the neutral he will be exterminating if it all goes wrong, it will be the poor sod in the shower or house when it goes kaput who will exterminated.... its okay though they might find his fingerprints all over the CU so guilty as charged your honour. I don't think he will be able to use the competent person defence!
 
This has gotta be a wind up by admin surely. 3yr checks, needing to change board, broken ring and the 16A light cct.... It's not making much sense at all. I'm not gonna bite again after this message.
 
Its not the neutral he will be exterminating if it all goes wrong, it will be the poor sod in the shower or house when it goes kaput who will exterminated.... its okay though they might find his fingerprints all over the CU so guilty as charged your honour. I don't think he will be able to use the competent person defence!
No finger prints as I wore my marigolds
 
Lmfao meant to say re-terminated that' Samsung auto correct for you and the fuse box is also being changed soon in the house as it's a plastic one.
Due to current regs with the 3 yearly check I am aware that being under the stairs that they now have to be metal and non combustible with current regs.

Will have to post a pic of my consumer unit in the property I rent you will all comment on that

what 3 year check?

Who says that they have to be metal?
 
what 3 year check?

Who says that they have to be metal?
Due to owning the house and renting out it needs to be electrical checked every 3 years and gas safety to be done each year maybe differet in other areas but here has to be complied with.
I know a few other landlords who have had to have consumer unit changed to a metal casing due to the new amendment regs being put in place so under current guidelines when the next inspection is due it will need to be changed and replaced.

Copy here of regs Consumer units - IET Electrical - http://electrical.------.org/wiring-matters/55/consumer-units/index.cfm
 
Due to owning the house and renting out it needs to be electrical checked every 3 years and gas safety to be done each year maybe differet in other areas but here has to be complied with.
I know a few other landlords who have had to have consumer unit changed to a metal casing due to the new amendment regs being put in place so under current guidelines when the next inspection is due it will need to be changed and replaced.

Copy here of regs Consumer units - IET Electrical - http://electrical.------.org/wiring-matters/55/consumer-units/index.cfm
Deleted due to I said I was out
 
...landlords who have had to have consumer unit changed to a metal casing due to the new amendment regs being put in place so under current guidelines when the next inspection is due it will need to be changed and replaced.

Reg.421.1.201 is applicable to new installations designed after 01/01/16 and there is currently no requirement to replace old plastic CUs with metal. However, I can see insurance companies picking up on this in the future and incentivising replacement with a discount (or should I say a smaller increase than otherwise), in the same way that if you have a monitored alarm system with RedCare, this greatly helps on home insurance costs, particularly on larger properties.
 
You know what don't care I can't here to ask a question just because I'm not qualified doesn't make me incompetent of knowing what I'm doing working with someone who's qualified from a young age and being overseen and checked on standards of work and also working on 3 phase and also being more than competent of doing so is more than some newly qualified electricians have in experience.
As most newly qualified electricians just goto college learn sit a test and have a certificate being trained alongside a family member rewiring houses at weekends and then working doing air conditioning from the age of 14 until I was 19 and being trained to a standard by a qualified person is more than anything on a piece of paper and all on this forum are so stuck up there as**s that I'll seek advice on a different forum
You asked a question of which the forum is here for but within few posts it was clear to members you are dabbling in things you are not competent to do, regardless of your onsite experience unless you understand the theory behind what you do then you are not competent to do it on your own, it is very evident from your responses you are far from competent, your using the wrong test equipment, you not following any recognised sequence of testing and you making guesses, replacing items and finding your still in the same boat, the most dangerous thing in our industry is a DIYer who thinks he is more competent than they actually are, 3yrs of college will be a massive eye opener for you then I would challenge you to come back and look back on this thread, trust me you would shake your head, considering you have a dad fully qualified I actually find it strange you have come to the forum after several failed attempts to rectify the issue, surely he would naturally be the first port of call especially with him having the correct test equipment.
You mention low water pressure caused the shower to overheat and tripped the circuit, you clearly are guessing again as showers have integral thermal overheat protection and this would operate if it overheated (not your mcb or rcd), this would either self reset or require replacement.

Like others have mentioned within the thread I also strongly advise you get a competent Electrician in to do the fault finding or aid you in finding it, as you have clearly shunned this advise on numerous occasions I only can come to the conclusion your ignorance to your own lack of competence is a danger to yourself, as the forum is here to give good safe advise.
I prefer the forum upsets and loses a member by giving safe advise than aid a DIYer who is clearly taking on more than we consider they are competent to do, your postings and remedies to your own situation are a massive beacon of your position and therefore on that note I am closing the thread!
 
Last edited:

Reply to Rcd advice needed faulty or fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
625
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
870
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
940
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
I’m going to call an electrician out on Monday, but curious if anyone has any ideas about this fault: I have a new kitchen fitted and two...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock