6
hi all,

I had my consumer unit upgraded by an eletrician and the test on the main socket circuit revealed their is a break somewhere on the earth wire so no continuity.

The eletrician had a quick look around and roughly located where it could be (somewhere under the floorboards between certain plugs) but decided that it would be a better option to downgrade the mcb to a 16amp instead of a 32amp and if we have any tripping issues we can separate the kitchen circuit so that reduces the load on the main circuit.
We are also lucky in that a lot of the kitchen appliances already run on a separate circuit so we may get away with the 16amp anyway.

My only issue is leaving the break, he assures me that it is safe and no real gain in finding the break and money would better spent on adding a new circuit for the kitchen if it is required.

Is this the best way to go in this situation?

Thanks
 
all depends. if the break means just that the cpc is not a continuous ring but all sockets have a cpc, then it's not a huge problem. if, however, 1 or more sockets have no cpc (earth) connection, then that is dangerous and requires urgent/immediate remedy.
 
Reading your post has the electrician split the socket ring circuit in the kitchen into two seperate 16A radial circuits?
if not, then i fail to see what benefit a 16A MCB can provide, other than increasing the max. value of Zs.
 
all depends. if the break means just that the cpc is not a continuous ring but all sockets have a cpc, then it's not a huge problem. if, however, 1 or more sockets have no cpc (earth) connection, then that is dangerous and requires urgent/immediate remedy.

I'm sure he did say all sockets are earthed although I'm not sure how he would have tested that. I'll probably give them a call tomorrow to find out all the details.
 
Reading your post has the electrician split the socket ring circuit in the kitchen into two seperate 16A radial circuits?

He hasn't actually done that yet, only if it is required. I assume he wants to wire in a new circuit into the kitchen so that can take some of the load.

We have a utility room which has its own circuit so the washing machine, fridge, clothes dryer all come of that.
 
Would also have to disconnect the live conductors between the sockets either side of the point where the break in the CPC has been found.
then he'd have to make 2 separate radials.
 
yes, that's what i meant. 2 radials each on a 16A MCB.
 
Being on the job they have a much better understanding of the particular installation than opinions from afar

Certification, although necessary for all installation work, it actually means little with regard the standard of the work carried out

Maybe be a little positive and give a little trust,at least they seem to know what they are doing
 
I am getting one (waiting on it)
Will this show all sockets are safe then?

Does the test need to be done physically on all sockets in the circuit or can it be done from the consumer unit?
If the work you employed the Electrician for, was swap the consumers unit, thats what the (EIC) Electrical Installation Certificate will show.
An (EICR) Electrical Installation Condition Report on the other hand, is advisable prior to changing a CU, to highlight any problems like the one he encountered with your sockets.
What prompted him to check the sockets, normal procedure, if an EICR is not requested would be to do a few tests to ensure the RCDs on the new CU does not trip unnecessarily.
 

Attachments

  • Best-Practice-Guide-1-Issue-3-.pdf
    1.2 MB · Views: 12
Being on the job they have a much better understanding of the particular installation than opinions from afar

Certification, although necessary for all installation work, it actually means little with regard the standard of the work carried out

Maybe be a little positive and give a little trust,at least they seem to know what they are doing

Thanks for the advice.

I do trust completely trust their advice (The guy who installed the unit was brilliant) I was just interested to have a second opinion on what other people thoughts were on the best route to take going forward but now I know as long as each plug has been tested then their is no issue with leaving the break in the circuit.
 
Thanks for the advice.

I do trust completely trust their advice (The guy who installed the unit was brilliant) I was just interested to have a second opinion on what other people thoughts were on the best route to take going forward but now I know as long as each plug has been tested then their is no issue with leaving the break in the circuit.
Not knowing how the Electrician dealt with the break in the cable, other than downgrading the MCB it's hard to tlee, but as Telectrix says each socket needs to be tested to confirm the presence of a cpc. Did he isolate the damaged cable completely?
 
To be honest, if hes gone to the hassle of identifying where the break is, sorted 2 radials @16 and is part of NIC then it should be good.

Perhaps email asking if he split the ring so you have it in writing whats been done.
 
Well as Des56 has said let us look on the positive side they have had a consumer unit upgrade which with RCD protection for the sockets and the installation has been left in a safer condition than before.If there is a break in the cpc in the ring final circuit what is the Zs at the highest points this may be still under the max Zs for the protective device.Personally, I don't like sockets in a room being fed from different circuits but that's only an opinion. Has the electrician taken off the socket front plates to see if it is as simple as a cpc that has come out? If not it could be a joint somewhere.
 
Presumably he has already had the socket fronts off to see if all the earths were connected properly.
I would of thought that he would of checked the end to end continuity before he carried out the board change though.
 
Not knowing how the Electrician dealt with the break in the cable, other than downgrading the MCB it's hard to tlee, but as Telectrix says each socket needs to be tested to confirm the presence of a cpc. Did he isolate the damaged cable completely?

I don't think he completely tracked it down, He knew at which point the socket was showing the issue but from there he mentioned having to remove floorboards.
The only other thing he mentioned was downgrading the MCB. I guess I should get on the phone to them tomorrow to find out the complete facts
 
I don't think he completely tracked it down, He knew at which point the socket was showing the issue but from there he mentioned having to remove floorboards.
The only other thing he mentioned was downgrading the MCB. I guess I should get on the phone to them tomorrow to find out the complete facts
I would!!
 
A certificate IS partof the works, therfore payment should not be made until certificate has been issued, in my opinion.

If it is specified prior to commencement of the works that certificates will be issued after payment is received then he won’t get it until he pays.

I always do this with new or one-off customers and it has helped me to get the money out of non-payers
 
If it is specified prior to commencement of the works that certificates will be issued after payment is received then he won’t get it until he pays.

I always do this with new or one-off customers and it has helped me to get the money out of non-payers
Agree it's away of getting payed Dave, but is it a legitimate method, more importantly is it legal to use this method of chasing payment, after all the customer could argue that, infact you haven't completed until you issue a cert, wouldn't like to argue that in a court of law, you do the work, part of that work is certification, sorry I have to disagree withholding the certificate until payment is, in my opinion a bad move, no offence intended.
 
Last edited:
Agree it's away of getting payed Dave, but is it a legitimate method, more importantly is it legal to use this method of chasing payment, after all the customer could argue that, infact you haven't completed until you issue a cert, wouldn't like to argue that in a court of law, you do the work, part of that work is certification, sorry I have to disagree withholding the certificate until payment is, in my opinion a bad move, no offence intended.

Originally I was advised to do it by an NICEIC assessor on an annual visit when I was a qualified supervisor, and I’ve done it ever since.

I don’t see why it shouldn’t be legitimate if it is made clear in the written contract or terms and conditions before the work starts.
I don’t spring it on customers at the end of the job as a surprise, I make them fully aware before I start.

Also I include inspection, testing and issuing the certificate as a separate line on my quotes (for a nominal sum), so I can, and have on occasion, invoice for everything but this item and get the bulk of the job paid before issuing the certificate.
 
Originally I was advised to do it by an NICEIC assessor on an annual visit when I was a qualified supervisor, and I’ve done it ever since.

I don’t see why it shouldn’t be legitimate if it is made clear in the written contract or terms and conditions before the work starts.
I don’t spring it on customers at the end of the job as a surprise, I make them fully aware before I start.

Also I include inspection, testing and issuing the certificate as a separate line on my quotes (for a nominal sum), so I can, and have on occasion, invoice for everything but this item and get the bulk of the job paid before issuing the certificate.
That is completely the opposite what they said when my previous boss used to keep the cert back until payment and I think it was a question put to them in their connections magazine. So what you are saying is if I am right is they pay for the work and could pay for the cert later?
 
That is completely the opposite what they said when my previous boss used to keep the cert back until payment and I think it was a question put to them in their connections magazine. So what you are saying is if I am right is they pay for the work and could pay for the cert later?
No the certificate IS part part of the work withholding the certificate until payment. is in my book wrong, like I said in my ealier post would hate to argue this point in a court of law.
 
Last edited:
No the certificate IS part part of the work withholding the certificate until payment. is in my book wrong, like I said in my ealier post would hate to argue this point in a court of law.

Disagree.

If the spark states on the estimate or quote that the Certificate will be provided once payment has been received, and the customer goes ahead on this basis then thats whats been agreed.

If said spark states nothing on the estimate / quote then I would expect the certificate to be provided with the invoice.

As for what BS 7671 suggests - thats purely guidance...
 
No the certificate IS part part of the work withholding the certificate until payment. is in my book wrong, like I said in my ealier post would hate to argue this point in a court of law.

Ive never been challenged on this legally, but I have got my money on a job where other trades never got theirs.
 
Disagree.

If the spark states on the estimate or quote that the Certificate will be provided once payment has been received, and the customer goes ahead on this basis then thats whats been agreed.

If said spark states nothing on the estimate / quote then I would expect the certificate to be provided with the invoice.

As for what BS 7671 suggests - thats purely guidance...
Agreed but a Judge would use BS7671 as a guidance aid, wouldn't He/She, but as said before if stage payments have been agreed by both parties, no arguments isthere.
Ive never been challenged on this legally, but I have got my money on a job where other trades never got theirs.
Thatsbecause other trades can't hold their client to ransom over a certificate.
 

Reply to Consumer unit upgraded - no earth continuity question? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
770
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K
Just looking to see if anyone’s had a similar job or has any other ideas. Got a consumer unit to upgrade, the current one is fitted inside an...
Replies
2
Views
852
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
Replies
21
Views
5K
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top