Discuss Consumer unit upgraded - no earth continuity question? in the UK Electrical Forum area at ElectriciansForums.net
Ccx295
hi all,
I had my consumer unit upgraded by an eletrician and the test on the main socket circuit revealed their is a break somewhere on the earth wire so no continuity.
The eletrician had a quick look around and roughly located where it could be (somewhere under the floorboards between certain plugs) but decided that it would be a better option to downgrade the mcb to a 16amp instead of a 32amp and if we have any tripping issues we can separate the kitchen circuit so that reduces the load on the main circuit.
We are also lucky in that a lot of the kitchen appliances already run on a separate circuit so we may get away with the 16amp anyway.
My only issue is leaving the break, he assures me that it is safe and no real gain in finding the break and money would better spent on adding a new circuit for the kitchen if it is required.
Is this the best way to go in this situation?
all depends. if the break means just that the cpc is not a continuous ring but all sockets have a cpc, then it's not a huge problem. if, however, 1 or more sockets have no cpc (earth) connection, then that is dangerous and requires urgent/immediate remedy.
Reading your post has the electrician split the socket ring circuit in the kitchen into two seperate 16A radial circuits?
if not, then i fail to see what benefit a 16A MCB can provide, other than increasing the max. value of Zs.
I'm sure he did say all sockets are earthed although I'm not sure how he would have tested that. I'll probably give them a call tomorrow to find out all the details.
He hasn't actually done that yet, only if it is required. I assume he wants to wire in a new circuit into the kitchen so that can take some of the load.
We have a utility room which has its own circuit so the washing machine, fridge, clothes dryer all come of that.
Would also have to disconnect the live conductors between the sockets either side of the point where the break in the CPC has been found.
then he'd have to make 2 separate radials.
yes, that's what i meant. 2 radials each on a 16A MCB.
Being on the job they have a much better understanding of the particular installation than opinions from afar
Certification, although necessary for all installation work, it actually means little with regard the standard of the work carried out
Maybe be a little positive and give a little trust,at least they seem to know what they are doing
I am getting one (waiting on it)
Will this show all sockets are safe then?
Does the test need to be done physically on all sockets in the circuit or can it be done from the consumer unit?
If the work you employed the Electrician for, was swap the consumers unit, thats what the (EIC) Electrical Installation Certificate will show.
An (EICR) Electrical Installation Condition Report on the other hand, is advisable prior to changing a CU, to highlight any problems like the one he encountered with your sockets.
What prompted him to check the sockets, normal procedure, if an EICR is not requested would be to do a few tests to ensure the RCDs on the new CU does not trip unnecessarily.
  • Best-Practice-Guide-1-Issue-3-.pdf
Reply to Consumer unit upgraded - no earth continuity question? in the UK Electrical Forum area at ElectriciansForums.net
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Just looking to see if anyone’s had a similar job or has any other ideas. Got a consumer unit to upgrade, the current one is fitted inside an...
Hi all, what is the best way to configure surge protection in domestic dwellings when you have multiple consumer units? Does each consumer unit...
4K
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...