Sep 13, 2016
598
53
1,203
London
Hi is this a normal MCCB or MCCB with RCD I’m unsure cause of the earth leakage relay thanks don’t really know the settings on relay I’m apprentice thanks
It’s sending sorry
I could be wrong Bradley, but as an Apprentice would an explanation of how an RCD works be of any help? Do you know the difference between an MCB now known as a CB and an MCCB? they are two different Animals. Are you undertaking any Training courses ? I ask because if you are then gaining acess to the training area would be of value to you, plenty of like minded Guys and Gals in that area, along with some very good mentors with years of experience. You could try posting for access to this area.
Reactions: Rpa07
I know how they work never come across this type of breaker before and not had much to do with earth leakage relays thanks
If that earth leakage relay trips the mccb then yes earth leakage protection has been added to it.
The earth leakage relay would connect to a shunt trip or undervoltage release fitted inside the mccb.
The sensing for the earth leakage relay is done by a type of current transformer which surround all live conductors and this measures the earth leakage.
The below pictures show the current transformer around all live conductors (the white ring) and the shunt trip on the side of an mcb, this particular unit is a 125A TPN socket outlet.
The bottom of the enclosure is full of water as the pictures were taken to record flood damage.
Reactions: Wilko
Is there any underlying reason to your original question @Bradley6969, are you just curious here or is there an issue you have been asked to address/look into?
View attachment 42535 View attachment 42536
Thanks for that so say I put it on test report I’d put 60947-2 160A but would you put anything else if earth leakage was added eg
Just curious came across it the other day and never had anything to do with earth leakage relays before like I came to this and looked at test report and was unsure if you put over current for this distribution circuit obviously 60947-2 160A but added leakage if you put any associated RCD
Reactions: Darkwood
Your profile says/indicates you have nil electrical qualifications, why would you feel confident or competent in issuing an electrical report?
I’m not I just want to know incase I come across in future
London
Main switch help please
Bradley6969,
robd,