Hi

I have a checkbox (CCB1), it does the continuity and insulation checks BUT how do I do the Loop and RCD tests with the checkbox which does not have these facilities on?

I have read that you should have a dedicated circuit to do the loop and rcd tests.

Can someone please explain in more detail please?

Instructions not very clear so a walkthough guide would be most welcome.

Chris
 
Last edited by a moderator:
Just install a dedicated, non RCD protected socket next to your CU and label it for test purposes only. As long as you test it with a recently calibrated meter first to prove the readings then you can use it to prove your meter.

Need to double check readings with a calibrated tester at regular intervals though, make sure they havn't changed
 
Just install a dedicated, non RCD protected socket next to your CU and label it for test purposes only. As long as you test it with a recently calibrated meter first to prove the readings then you can use it to prove your meter.

Need to double check readings with a calibrated tester at regular intervals though, make sure they havn't changed


Hi Lenny,

How comes I have to use a Non RCD socket??

I thought it has to be a socket which is RCD protected?

Chris
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Calibration Checkbox CCB1
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
2

Thread Tags

Tags Tags
calibration

Advert

Thread statistics

Created
chrisgc,
Last reply from
chrisgc,
Replies
2
Views
3,170

Advert