Discuss I'm not sure if the Regs allowed separately bare earths. in the UK Electrical Forum area at ElectriciansForums.net

sham

-
Reaction score
72
I've been on this job to do an inspection before fitting a new RCD OR RCBO board. In most of my career until now the CPC is inside the T+E cable. This property has a separate CPC all through out the building. Only where there has been modifications, modern wiring has been used. If I can prove the ZS is good, is it ok to connect to this system. It's seems to be mainly the lighting that is wired in single sheathed cable which has been ran in conduit. I am hoping if anyone has any information regarding the regs about separate bare earth running through the property. There is a risk of borrowed neutrals if changing to an rcd or rcbo board. The customer does not want a Rewire but wants spots fitted and sockets moving. I have convinced him to change the board, now I am worried about nuisance tripping. However if you could advice about the earth mainly would be a great help. Personally I feel the wiring was good for it's day.

IMG_20181017_102010958.jpg
 
Sticking my neck out here I’d say of course Because regs are not retrospective as long as all the tests are good and you comply with the current regs regarding RCDs etc I don’t really see it as any different to connecting to Red and black PVC.
 
Last edited:
Where does the earth originate ? In my experience separate bare cpcs like this are often connected to lead water pipes as a means of earthing.
Never actually seen that but good point. As long as the earth does actually come from the CU/fusebox and not the water pipe and all of the tests are ok I don’t see a problem.

Obviously upgrading the bonding as well when replacing the board
 
Seen it most where rubber twin (no cpc) was used, either VIR twin or TRS. Bare cpc was often taken from a lead pipe, either soldered on or clamped on, and taken individually to sockets.
Found this in the ceiling also was interfering just with my continuity test, traced the wire back to this . 1mm cable connected and two lead cables of 2.5. It was a stressful day lifting floor boards.

IMG_20181017_100309007.jpg
 
Found this in the ceiling also was interfering just with my continuity test, traced the wire back to this . 1mm cable connected and two lead cables of 2.5. It was a stressful day lifting floor boards.

View attachment 44941
Is that the guts of an old thorn 8ft brings me back to the first few months of my apprenticeship taking down these old lumps and replacing them with 6fts and I mean lumps just about a 2 man lift to get the bloody thing down:screamcat:
 
Is that the guts of an old thorn 8ft brings me back to the first few months of my apprenticeship taking down these old lumps and replacing them with 6fts and I mean lumps just about a 2 man lift to get the bloody thing down:screamcat:
Well, this is under the upstairs floor board and two cables come out, they felt cold and are metal, never seen anything like it. These metal cables go to the end of a roof end, loft. (It is a bungalow) they end up in junction boxes that go nowhere else. Diconnected
 
I’d disconnect the bonding and the bare earths from the board and do an R2 on the bare earth from the end at the board to ensure its complete and then again at the bit your going to connect into and to the board itself and then the pipes themselves just to rule out that the bare earth was coming from elsewhere I reckon if you do that you’ve pretty much proved beyond reasonable doubt that the earth is suitable and actually coming from the CU and not the pipes or anywhere else.
 
Well, this is under the upstairs floor board and two cables come out, they felt cold and are metal, never seen anything like it. These metal cables go to the end of a roof end, loft. (It is a bungalow) they end up in junction boxes that go nowhere else. Diconnected
Old lead cables probably wonderful stuff :rolleyes: the rest of the cables in the house aren’t lead are they?
 
Old lead cables probably wonderful stuff :rolleyes: the rest of the cables in the house aren’t lead are they?
Now you mention it, how would I know if the lighting cables are lead. I just assumed they are copper. The system is mixed. The sockets are wired with stranded cables here and there, as long with the lights. There has been changed since.
 
2.5mm Lead cables?!?

There's many miles of the stuff still in use in Devon, some in terrible condition. Have some old magazines here that stated a safe working life of only 10-15 years

Am I right in thinking freddo TRS is the thick black rubber sheathed stuff that's a real nightmare to cut?

And VIR is the cloth/cotton covered singles?
 
2.5mm Lead cables?!?

There's many miles of the stuff still in use in Devon, some in terrible condition. Have some old magazines here that stated a safe working life of only 10-15 years
Horrible stuff i remember a few years ago attending a fault that was caused by the lead sheath being compressed and nicking the cores couldn’t for the life of me figure out what it was as someone had replace the CU and Extended the lead with PVC o_O
 
Now you mention it, how would I know if the lighting cables are lead. I just assumed they are copper. The system is mixed. The sockets are wired with stranded cables here and there, as long with the lights. There has been changed since.

Lead cables have an outer sheath of lead.

If the conductors of the cables you're looking at appear silver, they are either tinned copper or if they feel very flexible but break easily, they could be aluminium.
 
Lead cables have an outer sheath of lead.

If the conductors of the cables you're looking at appear silver, they are either tinned copper or if they feel very flexible but break easily, they could be aluminium.
They are not weak, but because I scraped the bare end because it looked dirty it seemed silver underneath, is this an issue ?
 
Lead cables have an outer sheath of lead.

If the conductors of the cables you're looking at appear silver, they are either tinned copper or if they feel very flexible but break easily, they could be aluminium.
They are not weak, but because I scraped the bare end because it looked dirty it seemed silver underneath, is this an issue ?
Yeah if they felt frozen they’d be lead sheathed just wondering if the rest of the wiring was the same don’t think aluminium was really ever a viable conductor here except in SWAs but @SparkyChick is right on how to identify it
All seem disconnected. That is the only lead I found.
 
Am I right in thinking freddo TRS is the thick black rubber sheathed stuff that's a real nightmare to cut?

And VIR is the cloth/cotton covered singles?
Not too sure on the TRS as I’ve never seen it but VIR is definitely the cloth cotton covered rubber kinda looks a bit like skanky iron flex but most of it that you’ve probably encountered has had the rubber completely disintegrate and fall off I worked for the council in my area years ago and encountered it in the town hall all crispy and horrid caused problems after problems but as far as I’m aware is still in service now because they didn’t want to pay to rewire it
 
To add... aluminium cable is a nightmare. I've done a couple of jobs where the conductors have been nicely dressed into the back box, but just taking the socket off has snapped them.

I think the aluminium becomes work hardened by merely bending it (like copper will) but more quicker. Hard metal normally means brittle metal, so you have to be very careful working with it.
 
To add... aluminium cable is a nightmare. I've done a couple of jobs where the conductors have been nicely dressed into the back box, but just taking the socket off has snapped them.

I think the aluminium becomes work hardened by merely bending it (like copper will) but more quicker. Hard metal normally means brittle metal, so you have to be very careful working with it.
And if the sheath is damaged or there is any damp the Aluminium will sort of corrode (oxidise)and significantly reduce the conductivity and mechanical strength
 
It's hard to say from a distance.

It all depends on what you scraped.
The wiring seems the old singles that go through galvanised conduits, the wires have grey sheath followed by red insulated wire. The red insulation seems good. The nuetrals outer sheath appears darker, could say black or like that because it's old followed by black insulation then bare wire. The cores are stranded and seem strong. And thicker than 1.5 mm.
 
The wiring seems the old singles that go through galvanised conduits, the wires have grey sheath followed by red insulated wire. The red insulation seems good. The nuetrals outer sheath appears darker, could say black or like that because it's old followed by black insulation then bare wire. The cores are stranded and seem strong. And thicker than 1.5 mm.

Sounds to me like double insulated singles. Imperial size. The conductor is most likely to be tinned copper.
 
Aluminium conductors in this country is common for distribution cables but for small scale stuff it became popular when copper prices rocketed in the 70s/80s and yes SC I have some off cuts:D. BICC (British Insulated Calender Cables) is the most common manufacturer to be found and it can be hard to spot as the aluminium conductor was copper clad so it appears to be copper. The chances of a lead sheathed cabled produced for UK use having aluminium conductors is less than zero although they may appear to be as they will be tinned copper.
 
All the ali stuff I've worked on here has been plain vanilla aluminium, didn't realise there was a copper clad version.

I remember seeing them putting new sub-mains in when one of my schools was being renovated. Big honking 3P+N SWA cables with quarter segments of aluminium in those oh so lovely colours.
 
Copper clad was generally restricted to the small scale T&E cables, it was made by placing an aluminium bar in a copper tube and stretching it to produce the conductor. Often only realised today when the conductor keeps breaking, common sizes were 1.5 solid and 4.0 stranded.
 
I have seen a few lengths of copper clad aluminium, I have some 7/.029 here somewhere. I have only once seen a house wired with solid aluminium cables, horrible stuff just breaks off when disturbed.
 
I have seen a few lengths of copper clad aluminium, I have some 7/.029 here somewhere. I have only once seen a house wired with solid aluminium cables, horrible stuff just breaks off when disturbed.
I suspect the 7/.029 is actually 4.0mm as I am pretty sure although not certain it was never produced under imperial sizes.
 

Reply to I'm not sure if the Regs allowed separately bare earths. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
578
This question has probably been asked several time but things change. The house I'm living in now was built in the 1960's and has a ring main...
Replies
15
Views
951
Hi, I have a book on domestic wiring which says that everywhere there is a change in current carrying capacity along a circuit there must be some...
Replies
3
Views
331
Now that SPD's must be fitted regardless, how does this stand from a sub-main perspective? Went to look at a job and they want a supply to a pre...
Replies
3
Views
2K
In a property with two consumer units one for the ring main etc., and the other for the 1970s storage heaters (storage heater CU looks like it’s...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock