A
Ashfoster96
Failed AM2 Fault Finding 3 times!!! hope somebody can help me, I’ve spoken with the examiner, he said my fault finding itself is fine it’s just my writing/explanation. Can someone give me some examples of what to write so I can pass it this time!? Thanks
Would you be able to provide an example of what you found and how you wrote it up?
Upvote 0
You just need to put into writing exactly how you found the fault and what tests you did to verify it. For example, if it was an L-N short you may have carried out an insulation resistance test at 500v and got a reading of 0.01 ohms which shows you have a dead short and so on. It's to show that you actually know what your doing rather than just finding the fault through luck.
Upvote 0
We are supplied with a continuity/high resistance tester, we have a full Meghan test kit for the test
Thanks, At our exam we only get supplied with a continuity/high resistance tester, from what some people have told me it’s much more simple than that but I appear to be working something wrong?
Upvote 0
Hi Tim, say for example it’s an open circuit between mcb and Switch fused spur for CO2 detector. I would write open circuit on the line conductor (brown) of FP200 cable between MCB at DB and switch fused spur.
Recommended remedial work:
• check cable for damage.
• Repair cable if possible.
• Replace/Re-wire cable if necessary.
• RE-TEST!
Upvote 0
• RE-TEST!
So in that example, I would expect:
Db reference if any
Circuit reference (which MCB)
Test that identified fault (R1 + R2 probably)
Result - infinite ohms
Further tests that identify its Line and not CPC which is broken , R1 + RN, and RN + R2
Results
Conclusion - R1 broken
Then as you said.
Maybe think in terms of what you’d write down for someone else has to come and repeat tests, confirm your results , fix it, and retest.
I might be way off but that would be my answer. Others who have done this more recently might be able to say if I’m on right lines or not.
Upvote 0
Hi, does anyone know how many faults you need to find for the AM2S ? Thanks !
Upvote 0
Upvote 0
Failed my AM2 fault finding 3 times….please help!?!?
Ashfoster96,
MJPD29,
Electrical Courses