Discuss Insulation resistance test on a damaged conductor in the UK Electrical Forum area at ElectriciansForums.net
Neptune
I have a 2 metre T&E cable. I applied a IR test (500v) across P and N to E with the other end of the cable safely sitting on the floor and it reported the meter maximum. As expected.
I then completely cut through the N conductor on the cable and repeated the test. It still reports the meter maximum. Can someone explain this result please and I am trying to reconcile it with a real life situation where there is a nail through one of the conductors.
Thanks in advance.
Thanks in advance.
If you have cut through the conductors then IR will be high - an open circuit is theoretically infinite impedance.
Think of what result you get when you perform an IR test with your leads disconnected from all conductors.
A lower IR would result if there was some interconnection between the two conductors, whether caused by moisture, cable damage etc.
When explained like that it makes perfect sense.
But...high reading and the meter maximum are regarded as good outcomes of the IR and its only when we have a lower reading (2 I think?) that we should investigate. Here, we have a broken conductor and the reading would be the meter maximum. Same as it would be for a perfect cable in the ring. I am sure I am missing something.
Your continuity tests would confirm whether a conductor is intact or not - if there is a break, you would investigate.
But what if there was a nail smashed into a conductor but not completely severed the conductor. Would that result in a pass on the continuity test? and does IR testing have any relevance to this situation?
The nail scenario will affect IR if it bridges between two conductors, or damages the insulation between the two conductors enough to cause them to touch/interact when the high test voltage is applied.
As Jim says, an open circuit is found with continuity tests.
sorry to be pedantic but what happens in the above situation. The nail has penetrated one of the conductors and not any others and also, hasn't completely severed this conductor.
If it has only penetrated one conductor and not touched any other then it is likely the IR test will be clear, ie read HIGH.
If it has completely severed the core then the continuity test of that core will fail open circuit.
And a “high” reading will also be obtained ina perfect situation too. Hence, you would merrily continue despite a nail being jammed into one of the conductors? Is this an unusual situation and a short coming of the testing?
You could test between the nail and the conductor and get a low IR reading!
But in practice a meter cannot know between an open circuit due to a break, or good circuit. When you think about it, a normal connection to a cable at any point (accessory, terminal block, etc) is basically a screw that squashes into it.
I suppose if the screw has penetrated a single core, the small r readings will be different (between L and N) and that could be a clue as part of the continuity test?
No, if only one core has been touched the continuity tests will be fine. Unless it has fully broken the core in which case continuity tests will be infinity, or maximum the meter can display
Thanks again. Final question please.
If there was a screw that has partially penetrated a single conductor, we have established that this will not be detected as part of the Continuity or IT test. You would walk away from this installation with a thumbs up.
Could this situation subsequently cause tripping etc.?
The principle is: if an IR test on a cable reads high, the cable might be good. If it reads low, the cable is definitely bad.
We are surrounded by insulating air, so in a dry environment there is no easy way to detect places where PVC insulation has been punctured or stripped as the air surrounding the cable will provide equally good insulation. In truth, in a dry environment where there is not much earthed metal around, IR tests will miss many kinds of damage. The problem is much more likely to be detected where something non-insulating is present to make contact with the exposed conductors; damp masonry, soil, dead wildlife etc. E.g. if a squirrel gnaws the PVC off a cable cleated along a wooden joist the loss of insulation itself won't cause a low reading. But if the carbonised dead squirrel ends up lying across the exposed conductors then the IR will show that up.
Does it matter? If a screw just grazes the line conductor in a cable then you have a live screw, but it won't shock anyone unless they touch it. There must be hundreds of thousands of live screws and nails around the world, bashed into dry timber and completely undetectable by normal testing. If the screw happens to be holding up a metal shower rail then it is a serious shock hazard, but it is likely to be in contact with various building materials, not all perfectly dry, so at that point the insulation resistance is likely to read low enough to earth to arouse suspicion. This is why it is so important for IR tests to be done with the CPC connected to the MET, unless specifically troubleshooting.
IR tests are very good at finding substandard insulation materials, water ingress and underground faults, because here the good insulators are replaced with bad ones, rather than with air.
You would definitely not walk away from it and leave it. Assuming of course you know about it. In practice you wouldn't know, unless you'd done it yourself
Very unlikely unless the screw was somehow earthed.
To put it another way - I've never had a tripping RCD where the IR test hasn't shown me which circuit is causing it and helped me fine the fault.
Out of interest which tester did you get?
Full dead testing includes
insulation test. Very high reading. To check that what shouldn’t be touching, isn’t.
Continuity test. Very low reading. To check that
What should be touching, is.
Continuity tests over several conductors that are the same length, and should be the same resistance can give clues to problems if the results are vastly differing.
Your example would be a “perfect storm” scenario where all test results are correct, but damage may make itself known at a later date
and why there should be periodic testing done on any installation.
Damage like this may not show straight away, but over a number of years.
Megger MFT 1711. Resolved my earlier issue. Will post an update.
Thanks for your help.
I have noticed that when doing the IR test, I have to hold down the Test button for several seconds before the meter reaches the maximum reading. It's not instant. Its that normal?
When completing or updating a Ring, are these the minimum tests:
1. Continuity test
2. Cross over / figure of 8 tests
3. Insulation Resistance test
Are there other mandatory ones?
Yes. There are two main mechanisms at work here: Capacitance and dielectric absorption.
The voltage source in the tester has a maximum output current of a few mA and only 1mA at the full 500v, so it takes a finite time to charge the capacitance of the installation. On a small circuit that would be within the settling time of the meter indication but a large circuit and/or connected suppression capacitors can give a noticeable delay reaching a steady value.
Then there is dielectric absorption. Insulating materials unavoidably contain some molecular dipoles that store charge by re-orientation, but this charge storage cannot be charged or discharged rapidly. When subjected to a voltage change, a tiny current continues to flow for a while while the charge is 'absorbed' into the material which can cause an insulation reading to rise slowly over a minute or so. The same effect occurs when discharged.
Yes it would.Your insightful questions highlight the limitations of our current testing equipment.Electricians cannot locate a conductor that is damaged but not severed.It is entirely possible that such a situation could occur and result in a "hotspot" due to high resistance.On the other hand such situations are extremely rare.
Reply to Insulation resistance test on a damaged conductor in the UK Electrical Forum area at ElectriciansForums.net
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Hi all , after some opinions on N-E fault or ring main. After chasing this fault and ruining my bank holiday weekend , ring main IR readings as...
Hi, I'm a little confused confused is someone can shine some light on the amendment 2 way of doing IR. I know you have to do one 1st fix at 500V...
Hi all, Testing question for you. I'm currently testing an existing domestic installation. The wiring is about 20-25 years old. We have rewired...