You should bond the array to a earth spike, the inverter can be earthed at the MET.

As for the RCD issue i think there will be a large debate very soon.
 
Just fired up a 10 panel HIT x 250w Sanyo and a 2500 HF inverter. The whole system has never got over 500w despite being running for 2 weeks. The system has produced 24 KWhours in tha time. Have spoken to SMA and they say its a sanyo problem. Sanyo say its SMA. Fault seems to lie with MPP trackers. Trying to get someone to admit liability.
Could anyone suggest a solution. Onther inverter maybe?? failing this I am taking all the panels off the roof FRiday and replacing with Schott or Hyundai. Got to get this fixed as the scaffold alone cost me £2000.00 and not prepared to leave a system that is prone to problems. Any help greatly received

Any update, on your situation? We have one system displaying this fault and we are preparing to swap the 2000HF for a Fronius like the original poster, however I would like to understand what is causing this, wasted a lot of time on this problem!
 
Ive just installed 14 x sanyo hde240 with sb3000-hf inverter. Only turned on friday. 10 kwh produced over the 3 days but its been cloudy and overcast here in Leeds. Saturday bright sunny day and got peak of 1.5kw. So does this sound ok or am i experiencing this syndrome? Ps fri 2.3kw, sat 5.7kw, today 2.6kw
 
Ive just installed 14 x sanyo hde240 with sb3000-hf inverter. Only turned on friday. 10 kwh produced over the 3 days but its been cloudy and overcast here in Leeds. Saturday bright sunny day and got peak of 1.5kw. So does this sound ok or am i experiencing this syndrome? Ps fri 2.3kw, sat 5.7kw, today 2.6kw

Sounds fairly low to me, hard to tell without knowing the exact weather conditions but would be worth looking at Sunny Explorer to check the charts.


Down in the SW with the sun out we spoke to a customer who has 15 235 Sanyo's (on a Fronius) and it was peaking over 3000W. The reason we were there was because we were doing test on his neighbours system that has the fault (10 Sanyo 235W and a 2000HF).
 
hi, i have web box installed so here is the url for the data: thorn Energy and Power
let me know what you think? i know weather has a big part to play, but i have a mate with aurora inverter and sharp mono's, 10 miles away from me with similar facing roof. he was away for weekend so will be comparing with his system from tomoz
 
Ive just installed 14 x sanyo hde240 with sb3000-hf inverter. Only turned on friday. 10 kwh produced over the 3 days but its been cloudy and overcast here in Leeds. Saturday bright sunny day and got peak of 1.5kw. So does this sound ok or am i experiencing this syndrome? Ps fri 2.3kw, sat 5.7kw, today 2.6kw

To give you something to very roughly compare with - we have just installed 16 x 250's on a West facing roof with a Power One inverter. Commissioned late on Friday afternoon - 13kwh by Sunday morning first thing.....
 
Doesnt look too good for me then. Will have to look at another inverter. Will give a few days and compare with my mate.
Thanks for help guys!!
 
just looking at inverters, have i read this right that the power one pvi3600 can be set to 2 trackers? this would be ideal as i have a chimney shade for a few hours in the mornings
 
12x SANYO HIT 240s on a SB3000HF. Single string, no shading. SSE facing roof at 42 deg tilt.
I have seen 2.5 kW in a single hour on a sunny day last week (remember it is October!). It has been producing over 9 kWh per day on average since install on 29/9/2011 in Sunny South Cambs :)
 
Just to confirm i will have to change my inverter aswell. Today 3.5kwh. My mates was 8.1kwh and he has 22xsharp mono connected to powerone inverter sim pitch and azimith direction. Lucky scaffolding is still up so now need to create 2 strings!!
Question to the experienced guys power one pvi3600 or the pvi3600outd? Thanks in advance
 
I'd go for the PVI 3600 if it is going in your garage or the PV 3.6 outdoor if it is going in your loft (or outdoors, obviously).

The PVI 3600 is a great looking bit of kit but the 3.6 outdoor looks to me like it will deal with heat better.
 
I'd go for the PVI 3600 if it is going in your garage or the PV 3.6 outdoor if it is going in your loft (or outdoors, obviously).

The PVI 3600 is a great looking bit of kit but the 3.6 outdoor looks to me like it will deal with heat better.

Thanks for that mate, the outdoor version it is!


Sent from my iPad using Tapatalk
 
Morpheus have you taken any adivce from SMA or sanyo on this issue? Have they been helpful or even contactable? I have not been ablt to get through to the UK team all week last week and they are not phoning back after leaving messages or responding to emails now.

Have had to speak to germany but then there's no continuity and i have to explain the whole saga from the very beginning every time i phone. I get the same things every time, 'have you checked the event codes' etc...

Really starting to get fed up with it all now.
 
to be honest ive not spoken to sma or sanyo purely because of the responses from the previous posts, ie they themselves didnt know what was happening. there are no error logs being reported by the inverter at all so i have nothing to go on with.
personally i am going for installing a new inverter as i am fortunate in that the scaffolding is still on the house so i am going to change the panel config from 1 string into 2.
 
No not any nearere solution. Have now replces Sanyo with Hyundai 250w panels but still got same problem. Short citrcuit test and voltage are correct to DC isolater but drops dramatically when going from this to the Inverter.
Any clues anyone ???
 
Any update, on your situation? We have one system displaying this fault and we are preparing to swap the 2000HF for a Fronius like the original poster, however I would like to understand what is causing this, wasted a lot of time on this problem!

No we have just replaced panels after speaking with SMA. Have now got Hyundai panels on. We still have the same problem. Voltage is correct and amps correct at DC switch. AS soon as it goes in to the inverter we are just getting 1.1amps and about 200w power. Have now checked everything. We even put on a fronius 20g inveretr. Looking for some help here. Off to replace DC switch tommorrow.
 
@ Morphues: I urge you to speak to SMA if you are having this problem. They don't seem to be taking it seriously enough. The germans are claiming not to even know about it by my last phonecall.

@Robert Carter: this is the first i've heard of the problem with a panel other than Sanyo. it suggests to me that rather than a compatibility issue it may be a faulty component of some kind? Has it been any better with the fronius?
 
Powerone online tech director knows of the issue and suggested to turn opti-trac on bu i couldnt find hat option on the hf inverter. He said on tl it does the trick. I will speak to ma tomoz but i also have a pvi36outd coming tomoz but wont be installing till weekend.


Sent from my iPad using Tapatalk
 
@ Morphues: I urge you to speak to SMA if you are having this problem. They don't seem to be taking it seriously enough. The germans are claiming not to even know about it by my last phonecall.

@Robert Carter: this is the first i've heard of the problem with a panel other than Sanyo. it suggests to me that rather than a compatibility issue it may be a faulty component of some kind? Has it been any better with the fronius?

No we have exactly same problem with fronius inverter.Tested all panels on install and short circuit all the correct readings from the array up to the DC isolater. It goes down hill after that
SMA have no idea or solutions to this problem but I suspect its not an inverter problem now as we have now tried 2 SMA 2500HF and a fronius inverter . All do the same
Not exactly impressed with SMA myself.
 
Powerone online tech director knows of the issue and suggested to turn opti-trac on bu i couldnt find hat option on the hf inverter. He said on tl it does the trick. I will speak to ma tomoz but i also have a pvi36outd coming tomoz but wont be installing till weekend.


Sent from my iPad using Tapatalk

Power One tech help were helping you out with an SMA problem?
 
Power One tech help were helping you out with an SMA problem?

Sorry it was power-store also known as ccl components. I mentioned it to one of their tech guys whilst i was ordering the inverter. He himself was unaware of the issue but his tech directer was and i got an email a few hours later. Soz for confusion


Sent from my iPhone using Tapatalk
 
i know there's big things going on now but i have another update to this thread which is contrary to some of my recent ones.

We had a call from the customer we swapped the SB3000HF out for a Fronius IG TL 3.0 today and the fault has reoccurred. Again a nice sunny day where it should have been going well.

This problem cannot be SMA inverters after this, it must be panel or DC wiring problem.

Not what we wanted to hear today after the EST business...
 
Hi all im new here Just completed my first install and hows your luck i installed 12x sharp nu 250 j5 pannels and an sma 3000hf invertor and i was ready for my first system switch on to find that i was only getting at max 1.2amps and around 400v spoke to sma and they said they had past it on to the germans to find out what was going on in the mean time they have sent out a replacement invertor which will be here tuesday i recomend to everyone stay clear of the sma 3000 hf
 
quick update i replaced my sma-3000hf yesterday with a power one 3.6 outd, so lets see what happens. again i am comparing with a mate of mine about 10 miles away
 
Inverter changed 10 days ago and now getting comparable generation readings compared to my friends. Only problem is no sunny days so cannot test properly. Last week 1 sunny day peaked at 1400w but that was the highlight. Every other day 1-2kw generated daily due to overcast cloudy drizzly conditions


Sent from my iPhone using Tapatalk
 
Hi BiggsSolar It didn't appear like that on the Fronius configurator unless I read it wrong. It also says: Please note: Module grounding at the Fronius IG TL not possible!

Module grounding is only an issue with Thin-Film modules whereby you must ground either the positive or negative DC cable. It is not possible on any TL inverter as far as I know due to the lack of galvanic isolation. i.e. by the very design of the circuitry
 
No we have exactly same problem with fronius inverter.Tested all panels on install and short circuit all the correct readings from the array up to the DC isolater. It goes down hill after that
SMA have no idea or solutions to this problem but I suspect its not an inverter problem now as we have now tried 2 SMA 2500HF and a fronius inverter . All do the same
Not exactly impressed with SMA myself.

Any joy in solving this issue?

We have had one system that is performing in the way described on this thread and having changed from an SMA to a Fronius the issue is greatly improved however still present on the odd occasion. The customer is being very patient but is keen to get it sorted in time for next year.

We are finding that the system is not loosing many kWh's of production due to this issue but they do find it very frustrating that on the brightest and highest producing days the system is under-performing.
 
Any joy in solving this issue?

We have had one system that is performing in the way described on this thread and having changed from an SMA to a Fronius the issue is greatly improved however still present on the odd occasion. The customer is being very patient but is keen to get it sorted in time for next year.

We are finding that the system is not loosing many kWh's of production due to this issue but they do find it very frustrating that on the brightest and highest producing days the system is under-performing.

Anyone got any updates?
 
Hi

I've just read all 9 pages of the SMA - Samyo panel issue and would like an update if anyone has any news. I have a 10 panel Sanyo HIT 250 system using an SMA2500HF inverter mounted outside on a north facing wall. The customer is reporting the same drp off of power which is rest to expected levels by switching the system off/on. Have reported the issue to SMA but heard nithing yet.

Solman
 
Hi

I've just read all 9 pages of the SMA - Samyo panel issue and would like an update if anyone has any news. I have a 10 panel Sanyo HIT 250 system using an SMA2500HF inverter mounted outside on a north facing wall. The customer is reporting the same drp off of power which is rest to expected levels by switching the system off/on. Have reported the issue to SMA but heard nithing yet.

Solman

'north facing wall' Seriously?
 
I do have something to add to this now, We have/had been working with Sanyo sending data from Sunny Explorer and screenshots from PV-Sol at the time the problems are occuring.

We do have some shading which i am willing to concede may be a contributing factor. Sanyo are saying that the shading is confusing the MPPT on the HF inverters causing them to bottom out and stay bottomed out.

SMA have said this may be a possibility and advised using Opti Trac, they gave us this advice in early Jan. The problem is we went to SMA with this issue in July and the HF series did not have Opti trac then or we would have tried it, as others on this thread have suggested. It is available now on HFs and can be retrofitted with a firmware upgrade.

All of this is very well and good but IF this is a shading issue, why does resetting the inverter, or even the DC isolators resolve it with NO change to the shade pattern? Sanyo have been very quick to deny all responsibility and sent out an email refuting claims made by installers on this and other forums, claiming there's no issues with their panels. They have been completely unable to answer the fundamental questions and just blame poor system design. I am not yet convinced.

One factor worth bearing in mind is the layout of the strings within each panel, the N series has parallel (geometrically) strings down the length of the panel while the H series has a band in the middle with two larger areas at each end of the panel. Each seperate string has its own blocking diode so the system can take shading if it is on up to 2 of the strings, if it covers all three expect a major reduction in output.

SMA have not helped much, other than to replace inverters with new inverters that do the same thing. Every time i phone for an update i have to explain from the beginning to someone new who asks all the same questions and who never gets back to me. As our customers were getting hacked off with us being unable to get answers we replaced the inverter with a fronius IG TL. The firmware upgrade with optitrac for the HF series came too late for us but i'd be interested to know if it works for anyone else?

The Fronius is behaving far better than the SMA did. My gut feeling on this after all the hassle is that there is some sort of incompatibility between the inverter(MPPT) and panel which is possibly exacerbated by shading.

I hope this helps and hasn't come across as too much of a rant, i appreciate that Sanyo and SMA have assisted us but i am still very frustrated that we have no resolution.
 
The solar panels have no moving parts, little in the way of fancy electronics and no intelligence; they just faithfully convert light to electricity. It seems hard to imagine how they could be the cause of the problem unless there's something wrong with their bypass circuits.

On the other hand; "artificial intelligence" - such as a inverter's (M)PPT - is only going to be as good as the program and processor which runs it. How many times have you played a computer which is generally hard to beat but occasionally it "artificial intellligence" makes a howler of a mistake?

I would put my money on it being an inverter processor/factory-programming hiccup. Perhaps it is occurring because quite a lot of inverters - even different makes - are using the same programming algorithm to run the (M)PPT? Perhaps the MPPT has not been properly tested in a part-shaded situation, since only an over-generous Feed-in-Tariff would encourage such inefficient deployment of solar PV as to put it in shady placed.
 
All of this is very well and good but IF this is a shading issue, why does resetting the inverter, or even the DC isolators resolve it with NO change to the shade pattern?
Resetting the inverter would have the same effect as using optitrac global peak because the inverter searches the full voltage range on start up, just as it does when using global peak (it's why the inverter output jumps around so much in the first few seconds after it starts up).

I can see this sort of problem happening on a system where shading started impacting on several strings of cells at once, eg a hard shadow from a chimney, TV aerial, soil stack etc sweeping up the array from the short side of one or more panels. This could easily place move the MPP outside of the range of the sweep of the standard MPPT system, and the output would reduce gradually from that point as the shading increased, because the MPPT would be still stuck at the old peak point and wouldn't move to the true peak point to allow the bypass diodes to function properly... something along those lines anyway.

Have you got any pictures of the array at the point where this problem was happening?
 
in response to a PM just thought i will provide a bit of update on this:
Since changing inverter to the powerone 3.6 outd i have had better output when compared with my friends. Recently had good sunshine and have had it peak at 2.8kw and no cutoff in production. I have never had to reset for any reason. So in my case changing inverter has worked for me. I managed to sell the sma that i took off and installed at a clients place with a chinese panel (cant remember off hand the name) and that is on south facing and performing fantastically aswell so inverter wasnt faulty just goes to prove that their was some sort of incompatibility. Hope this helps
 
Last edited by a moderator:
Righto, my last word on this (i sincerely hope). I'll post it in both threads so subscribers to both will see it.

After some great advice from member of this forum and some further digging with Sanyo, SMA and Fronuis we have been able to close this issue off.

As has been suggested by members here the large instantaneous drop in voltage caused by the operation of the by-pass diode on the Sanyo H-Series panel drops the array voltage outside the MPP trackers scanning range causing it to get stuck on a false peak. Its is particularly problematic with the H-series due to the large number of cells in the two end sections. See image:

View attachment By-pass configurantion H, N.pdf

I have been told that SMA's opti-trac was developed as a direct result of this known issue with their tracker. It is worth noting that this information did not come from SMA, they denied all along that the problem was anything to do with their product, they did not advise us to try optitrac when it became available and as far as i know did not release any info publicly in response to a problem that was being reported several time a day at its peak.

Fronuis were unable to offer an update similar to optitrac as they have not had the problem frequently enough to warrant it. We have now installed the third 3000HF, this time with opti-trac and the problem has been resolved.

I must be clear that this is not a fault with the panels or inverters as such, they work as they are designed to. The problem is one of compatibility, a specific panel, inverter and shade combination is the cause and removing any one of the three will resolve the issue. Opti-trac rescans at set intervals and therefor doesn't allow the tracking of a false peak.

I'm glad to have this resolved finally and would like to thank everyone of the forum who offered advice and also SMA, Fronuis and Sanyo for taking it seriously and coming up with some answers.

Finally i would advise anyone with H series panels and hard shading to monitor their system closely, part shading doesn't automatically mean poor performance and we have seen the system perform at near peak with the shading when the tracker is working correctly.

If you are considering PV and you have a shading issue get a quote from an installer who uses PV-Sol or equivalent who can model the system and quantify the imact the shading will have. I do wonder how many other systems are out there with this issue that has yet to be noticed.

Over and out...
 
good to hear. Do I get a gold trouble shooting badge?

interestingly, we appear to have a very similar problem that's been reported by a customer with sanyo N series panels on an older SB2500 inverter that as far as we can work out didn't have any shading at all.

I shall be investigating once they return from holiday.
 
I have this combination and dont have an issue at all, although my shading is different as its not partial but fully both before 9am and 4'sh
 
I reckon you should get two!

Well done Gavin. It was a nightmare of a problem and we'll all have an idea what to do if it happens in the future.

Indeed, thank you Gav, strangely enough both Sanyo and Fronius came up with essentially the same prognosis as you in the same week! I couldn't possibly say that they saw your posts but we know they watch this forum... ;-)
 

Reply to Compatability issues with SMA HF and Sanyo panels in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi all, total newbie to the forum. I sincerely hope that those in the know-how would be able to assist me. On my semi-detached house we have an...
Replies
13
Views
2K
My system has had an intermittent problem for the last few months. The inverter has occasionally been reporting PV Voltage Too High, then it would...
Replies
13
Views
5K
R
As someone with a keen interest in solar I am a long term loiterer on this forum, so thought it was time I joined. I also have a puzzle I can't...
Replies
6
Views
2K
N
I have a 3KW system which I have been having problems with since installation. Originally I had an SMA inverter but the problems were still the...
Replies
53
Views
8K
V
Hi - Im new to the Forum (today!) but have concern. I'm bit of a dumb blond when it comes to this stuff but here's hoping you guys might be able...
Replies
5
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock