Yes but if you issue a certificate showing a circuits details and results, it should reflect the whole circuit, not just the "new bit"
 
yes it states that all of the conditions of SECTIONS 631 and 632 shall apply to all the work of the addition or alteration, so if you read 631.3 which is in SECTION 631 it says an MWC may be provided for each circuit altered or extended.

the CIRCUIT i.e the whole thing

it doesnt say you can just test the new bit and to hell wether or not you have just connected up to an unsafe installation!!!!
 
Last edited by a moderator:
yes it states that all of the conditions of SECTIONS 631 and 632 shall apply to all the work of the addition or alteration, so if you read 631.3 which is in SECTION 631 it says an MWC may be provided for each circuit altered or extended.

the CIRCUIT i.e the whole thing

it doesnt say you can just test the new bit and to hell wether or not you have just connected up to an unsafe installation!!!!

Interesting, and I understand the point you are making. However, using the same example, lets say I connect a smoke detector to a lamp on a lighting circuit, but not to the lamp at the end of the radial circuit. What do I measure to enter a value for R1+R2 on the MWC?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Testing
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
23

Advert

Thread statistics

Created
hous1,
Last reply from
EastAnglian,
Replies
23
Views
3,036

Advert