C
cristafar
Working for a fire alarm company and we have to link 2 cb200 conventional panels one in a pub and one on next floor for the accommodation. There is 2 2cores running between the panels they just need connecting up. Here is the panel information PDF to see the terminals in the panel: http://www.acornfiresecurity.com/im...nd Commissioning Manual acornfiresecurity.pdf
was just wondering if someone could give me a heads up to where the cable connect too and why, just so when I go to the job with the Jurassic spark I work with I can understand it a bit more.
Thanks guys.
Class change is one way but will not show a zone or indication on control panel, it will just sound sirens.
Best way is to use zone 1 set as non latching via other panel`s relay, using 470 resistor. This way the end user knows zone 1 is the flat. And the flat user knows his zone 1 is the pub, see section 4.5 in cb200 manual, if you need wiring diagram just ask.
Thanks tazz just read the manual 4.5 and yes that sounds much better, for obvious monitoring purpose. At least then they will know if it is the upstairs or downstairs panel that as activated. A wiring diagram would be fantastic, with that then I can get it into my head and understand it better. Thanks for your replay and time
Chris.
Omit fault relay if not required, but will show cable or panel faults if used.
CB200 omits relay output automatically to prevent lockup, other panels you will need to program relay omit on zone 1.
Thanks for the info and diagram. That helps alot and I can see how it works now cheers. I'm sure the senior spark will be amazed when ask him if I can have a go at wiring it and come up with the above :).
Reply to Fire panel link. in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net
Good evening! Don’t have a huge deal of experience with fire alarms but having to work on a conventional system at the minute with various...
The big stately home I’ve been working in has an EMS 5096 alarm system with over 100 detectors and 3 (that I know of) panels. All detectors are...
Hi, I need to extend a fire alarm, the panel is a CTEC CFP 2 zone one and currently it has a couple of apollo alarm sense sounder bases/heads on...
4K
On this commercial building we are refurbishing it has the above fire alarm panel which I think is pretty much brand new, I'm not even sure it was...
I'm about to order this wired smoke alarm system as it can network but I just went to see how my existing fire alarms are hooked up and there...