We completed a garage conversion which involved Building Control. As part of the conversion, 3 new sockets were installed into the existing ring main and new spotlights daisy chained from the existing lighting circuit. An NICEIC-registered electrician undertook the work, invoiced for it, and said he would send the Part P certificate.

That was 2 months ago and we have not received the certificate or paid him despite countless phone calls on his mobile and landline, emails and text messages. All of his telephones ring (without immediately forwarding to voicemail) and his emails do not bounce. We simply cannot get hold of him.

A fellow Electricians Forums member proposed we have an Electrical Inspection Condition Report (EICR) undertaken, for a fee of £150. He said that this situation is not uncommon (!?) and he has never had a Local Authority refuse an EICR in such scenarios.

Having spoken to Building Control, they will only accept having the work 'tested' by their own sub-contractor and want a fee of £380 for this 'regularisation' work. We queried whether our newly found electrician can undertake the same 'tests' that their sub-contractor would and obviously at a much more sensible price. Their response was a firm 'no'.

Do we have any options available to us other than pay Building Control this extortionate fee? Surely they can't get away with charging such disproportionate amounts for work that any other competent person could do at the correct market price?

Any advice would very much be appreciated.
 
Last edited by a moderator:
Re: No Certificate For New Electrics And Local Authority Demands Read more: http://

I'm afraid if that is the stance of your LABC, you dont have any other option.

Consider contacting trading standard re; the un-obtainable electrician.
 
Re: No Certificate For New Electrics And Local Authority Demands Read more: http://

a point comes to mind here.

if the work did not involve new circuits, and it's not a special location (bathroom) or kitchen, then it's not notifiable to BC.
 
Re: No Certificate For New Electrics And Local Authority Demands Read more: http://

a point comes to mind here.

if the work did not involve new circuits, and it's not a special location (bathroom) or kitchen, then it's not notifiable to BC.
This was a garage converted into a living room. Upon mentioning your point to BC, their policy (apparently) states that any electrical work requires certification. Is there a written law somewhere that states a LABC cannot demand a certificate?
 
if BC were involved, as in planning , then they would require a certificate from a qualified spark , but most BC's don't bother if there have not been new circuits added.
 
Part P of the building regs state what is and is not notifiable.

AS far as the work is concerned a Minor Works should be acceptable which is a certificate (MEIWC) IMO.

Also have you taken this up with the NICEIC if he is useing their logo!



Sent from my Nokia 3330 brick
 
tell building control to shove it up their jacksey.
then remind them that under the EU freedom of labour & restrictive practices laws they have no legal power to insist you use one contractor over another , especially as youre a private property owner.
hire a electrician in a domestic installer scheme , they'll have to accept his certs.
 
  • Like
Reactions: 4 people
if BC were involved, as in planning , then they would require a certificate from a qualified spark , but most BC's don't bother if there have not been new circuits added.
Are you referring to a Part P Certificate or an EIRC?
 
As these seem to be" additions " this will not be notifiable. As has been said if no new circuits have been added or the Circuit protective device has not been altered it will not be notifiable.

Planning Portal - Approved Document P


Particularly read the parts on non notifiable work. This is the document that the LABC must work to. The rest is folklore.
 
tell building control to shove it up their jacksey.
then remind them that under the EU freedom of labour & restrictive practices laws they have no legal power to insist you use one contractor over another , especially as youre a private property owner.
hire a electrician in a domestic installer scheme , they'll have to accept his certs.
Does this apply if we are the contractor, and not the property owner where the work was undertaken?
 
eh ? so youre not the homeowner then ?
No. We are a contractor (general builder) who sub-contracted this sparky.

We have since let the homeowner (our client) know of the current situation. Thankfully they are more than sympathetic and are giving us the time to find a good solution.
 
Three theads all on the same subject?
All could have been rolled in to one.
Sorry Tony, I don't intentionally mean to make a forum 'mess' of threads. However I saw this and the other thread as entirely separate questions. Bunging them all together would create a far too long opening post.
 
labc do seem to get confused , which is a worry.... they all ways insist on timer fans too which acording to the elctricians guide to the build regs are only needed if the bathroom does not have a openable window
 
Are you sure he was NIC registered? It seems loads of people claim to be, and even put the logo on their stationary and van, but it turns out they're not.
 
No. We are a contractor (general builder) who sub-contracted this sparky.

We have since let the homeowner (our client) know of the current situation. Thankfully they are more than sympathetic and are giving us the time to find a good solution.

to be honest , the battle with the council needs to taken up by the property owner
theres only so much you the contractor can do.
have planning fees been paid for the conversion ?
if they have i wouldnt be handing over a penny more.
 
labc do seem to get confused , which is a worry.... they all ways insist on timer fans too which acording to the elctricians guide to the build regs are only needed if the bathroom does not have a openable window

All depends who you speak to at BC.....which is even more of a worry. They seem to know as much about the regs as many of the "experienced, fully qualified electricians" we get on here at times....
 
  • Like
Reactions: 1 person
i can't understand why they want any certificate if the electrical work is non-notifiable. the home owner should have a Minor Electrical Works Installation Certificate, but that's all.
 
That was 2 months ago and we have not received the certificate or paid him despite countless phone calls on his mobile and landline, emails and text messages. All of his telephones ring (without immediately forwarding to voicemail) and his emails do not bounce. We simply cannot get hold of him.

A fellow Electricians Forums member proposed we have an Electrical Inspection Condition Report (EICR) undertaken, for a fee of £150. He said that this situation is not uncommon (!?) and he has never had a Local Authority refuse an EICR in such scenarios.


Surely you are quids-in even if you do have to pay £380, as you haven't had to pay the sparky.
Btw, make sure you speak to the senior officer at LBC.
 
They seem to know as much about the regs as many ....

but they allow plumbers and builders to get away with murder.


 
i can't understand why they want any certificate if the electrical work is non-notifiable. the home owner should have a Minor Electrical Works Installation Certificate, but that's all.

It sounds to me like they are saying that it needs certifying by the electrician that carried out the work, not notifying. However, as he is incommunicado, this cannot occur. Therefore, they have to step in and make sure it is "up to regs", hence the fee.
Surely, if he invoiced you, you know his address. Pop and find out what's going on.
 
As these seem to be" additions " this will not be notifiable. As has been said if no new circuits have been added or the Circuit protective device has not been altered it will not be notifiable.

Planning Portal - Approved Document P

Particularly read the parts on non notifiable work. This is the document that the LABC must work to. The rest is folklore.
The piece relevant to us would be:

"Work that is not in a kitchen or special location and does not involve a special installation and consists of:
  • Adding lighting points (light fittings and switches) to an existing circuit [Only if the existing circuit protective device is suitable and provides protection for the modified circuit, and other relevant safety provisions are satisfactory.]
  • Adding socket-outlets and fused spurs to an existing ring or radial circuit [Only if the existing circuit protective device is suitable and provides protection for the modified circuit, and other relevant safety provisions are satisfactory.]"

However, as the ring was extended around the room and thus new cable was run to these sockets, does this not go against the following:

"Replacing any fixed electrical equipment (for example, socket-outlets, control switches and ceiling roses) which does not include the provision of any new fixed cabling."
 
It sounds to me like they are saying that it needs certifying by the electrician that carried out the work, not notifying. However, as he is incommunicado, this cannot occur. Therefore, they have to step in and make sure it is "up to regs", hence the fee.

not having a go at you , but thats not the point.
the work can be verified as satisfactory by any competant person - for alot less than nearly £400.
 
Are you sure he was NIC registered? It seems loads of people claim to be, and even put the logo on their stationary and van, but it turns out they're not.
Yes. A call to NICEIC this afternoon confirmed he is 'still' registered.
 
not having a go at you , but thats not the point.
the work can be verified as satisfactory by any competant person - for alot less than nearly £400.

I agree biff. Just trying to make sense of their logic here. The law as it stands states that you cannot certify someone else's work (unless you are the QS of that person), so if BC feel they have to follow that rule then in their opinion they have to inspect it themselves.
 
to be honest , the battle with the council needs to taken up by the property owner
theres only so much you the contractor can do.
have planning fees been paid for the conversion ?
if they have i wouldnt be handing over a penny more.
Planning was not required for the work. However Building Control was, which we paid for and organised on behalf of the client.
 
I can't believe the fiasco that is Part P

Up in Scotland the fees are set Scotland wide and the Buliding Standards accept NICEIC or SELECT (and sometimes other) certificates
 
The piece relevant to us would be:

"Work that is not in a kitchen or special location and does not involve a special installation and consists of:
  • Adding lighting points (light fittings and switches) to an existing circuit [Only if the existing circuit protective device is suitable and provides protection for the modified circuit, and other relevant safety provisions are satisfactory.]
  • Adding socket-outlets and fused spurs to an existing ring or radial circuit [Only if the existing circuit protective device is suitable and provides protection for the modified circuit, and other relevant safety provisions are satisfactory.]"

However, as the ring was extended around the room and thus new cable was run to these sockets, does this not go against the following:

"Replacing any fixed electrical equipment (for example, socket-outlets, control switches and ceiling roses) which does not include the provision of any new fixed cabling."

IF you altered the circuit then that s a different situation . Did you alter it:devilish:.
 
i can't understand why they want any certificate if the electrical work is non-notifiable. the home owner should have a Minor Electrical Works Installation Certificate, but that's all.
But can anyone issue a Minor Electrical Works Installation Certificate, even if they had not undertaken the installation themselves?
 
IF you altered the circuit then that s a different situation . Did you alter it:devilish:.
Here is a very rough sketch of what work was carried out. Is this classed as 'alteration' in terms of the Part P regulations?

Electrics In Conversion.png
 
But can anyone issue a Minor Electrical Works Installation Certificate, even if they had not undertaken the installation themselves?

As I have already said, I think this is what BC are getting testy about. Any competent person can carry out non-notifiable work, but it must be that person who certifies it. As this has not happened, they want to check it themselves.
 
However Building Control was, which we paid for and organised on behalf of the client.

really ???
then you've already paid the fees and all that is required now is the paperwork.
if it was me , i'd get a EICR done for the circuits that were worked on by a part p spark.
give report to homeowner and get him to hand it over to BC and do nothing.
you've complied with regs so sit back and let them take the next move.
 
As I have already said, I think this is what BC are getting testy about. Any competent person can carry out non-notifiable work, but it must be that person who certifies it. As this has not happened, they want to check it themselves.
In which case, do they have a leg to stand on in terms of forcing us to use their own sub-contractors and charging a ridiculous amount for the 'privilege'?

And when you say "that person who certifies it", are you referring to issuing a Part P cert or something along the lines of an EICR?
 
dont even need to be a part p spark , cant see why this has become such a big deal
as said get a EICR done
 
really ???
then you've already paid the fees and all that is required now is the paperwork.
if it was me , i'd get a EICR done for the circuits that were worked on by a part p spark.
give report to homeowner and get him to hand it over to BC and do nothing.
you've complied with regs so sit back and let them take the next move.
If at all possible, we would rather get everything signed off on behalf of the client (homeowner), as that is what we agreed to do and is part of our entire building service.

Can we just confirm that the electrical work is in deed not notifiable? (I have attached a diagram above)
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
No Certificate For New Electrics And Local Authority Demands
Prefix
N/A
Forum
Electrician Forum
Start date
Last reply date
Replies
75

Advert

Thread statistics

Created
TMess,
Last reply from
Guitarist,
Replies
75
Views
9,487

Advert