O
overskilled
So running a supply out to the shed to run a socket and a light (small small shed....garage to come later when funds allow) as putting tools away with the aid of a head torch is a pain in the posterior and finding stuff after dark is a nightmare.
Using some leftover 3 core 1.5mm2 XLPE SWA, only available run is along the fence (4x4 wooden posts concreted in, with timber 2 x 3/4 runners and 3x1 timber slats...its not going anywhere). Can't go under ground as manhole covers in the way (seemingly every house I live in has the streets drains running through the gardens....)
According to the book....the current capacity of 1.5mm2 XLPE SWA should be around 27amps clipped direct, so my thinking at the moment is to gland the SWA off to the outside socket thats part of the small kitchen ring final, use the SWA armour as the CPC, sleeve the grey core blue as a neutral and take 2 separate line feeds using the black (sleeved brown of course) and brown cores, Adaptable box outside the shed into 2 separate T+Es through shed wall and trunking/conduit inside shed to protect the cable where needed) black core to feed a 3A SFCU for a light and the brown to feed the socket as a spur.
Only issue thats nagging me is the shared neutral between the 2 line feeds (load at the shed socket will be at the very most 13amps (single power tool use and maybe a radio, at worst I'll stick an FCU in at the shed end) ), though its on the same circuit so shouldn't present a problem if I have my head screwed on right today (which after the dreaded dentist visit today isn't entirely guaranteed)
Thoughts?
yer shoud be good
i'd nenver trust the amour as cpc alone what happens when the cable get pulled or knocked and comes outof the nut
yer shoud be good
Why wouldn't you trust it? There's nothing wrong in using the armour as long as it's been correctly sized and the chances of it coming out of a gland are nil as long as it's been done correctly.
What are your thoughts on conduit or trunking as a cpc?
Reactions: 4 people
Are you saying you don't fit the glands properly and secure the cable properly such that it is protected from that happening?
The circuit described sounds like a bit of a nonsense to me.
Fit a switch fuse next to the external socket and run your shed supply from that, then you can switch it off when the dampness sets in.
I haven't go the books to hand but where did the 27A rating come from, if that's the rating for 90degree cable its no good as the terminals you are connecting to are only going to be rated for 70 degrees so you need to use the rating for 70degree cables.
Take the SWA in to a m/c twin socket in the shed and fit a switch fuse with 3A fuse for the light.
never tried it
Just because you haven't done something it's not feasible?
As long as the cable is fixed securely and glanded off properly then the chances of it being loosened are just about nil mate.
Reactions: 4 people
conduit or trunking as cpc i take it you were talking about metal and not plastic
To me this is a recent thing as long as the armour is Electrically & Mechanically (14th edition)sound then its good to go plus I would not discount it as a majority of installations have this plus there is nothing wrong with it .
What would you do on a CU change when the lights are run in conduit and it is getting used as an earth or a swa supply to the garage
There was a period (and probably now) when firms ran an earth wire alongside the swa because they were ignorant and did not know that 99.9 + per cent of the time the armour complied.
Shed supply
overskilled,
Bobster,