Discuss RCD tripping on lighting circuit when lamps (bulbs) are put into light fittings in the UK Electrical Forum area at ElectriciansForums.net

H

heartofgold

Hi,
Lighting circuit trips the RCD.
took out all the lamps and it holds. Put any lamp back into any light on the circuit and it trips. All but one of the light fittings on the circuit are Class 1.

Any advice gratefully received

hog
 
Are you an electrician? Has there been any alterations recently?
Sounds like a neutral problem to me.
 
Are you an electrician? Has there been any alterations recently?
Sounds like a neutral problem to me.

Yes I'm a spark. Yes the property owner fitted new accessories! Told me there was a problem with the tw way switch on the landing/hall before I started.
Going back this afternoon and I'll take all the lights down first and work back from there
 
Yes I'm a spark. Yes the property owner fitted new accessories! Told me there was a problem with the tw way switch on the landing/hall before I started.
Going back this afternoon and I'll take all the lights down first and work back from there
try starting at the switches...

- - - Updated - - -

Oh yes, but the DIY forum helps a lot here, some of it goes there first now lol
well alls i can say mike is this `net` has a bloody big rip in it...
 
Hi,
Lighting circuit trips the RCD.
took out all the lamps and it holds. Put any lamp back into any light on the circuit and it trips. All but one of the light fittings on the circuit are Class 1.

Any advice gratefully received

hog



I am interested in the thought process which led to you taking all the lamps out when faced with an RCD that wont hold. I have to admit that in the hundreds of instances I've been faced with this problem over the years not once have I thought to myself...."I know,I'll whip all the lamps out"
 
when will customers realise that it's £40 to fix the light, £60 if he watches, and £80 if he's messed with it first.
 
I am interested in the thought process which led to you taking all the lamps out when faced with an RCD that wont hold. I have to admit that in the hundreds of instances I've been faced with this problem over the years not once have I thought to myself...."I know,I'll whip all the lamps out"
dont waste your time here Wire...
its like talking to an apple or summat..
 
when will customers realise that it's £40 to fix the light, £60 if he watches, and £80 if he's messed with it first.

Many, many, many moons ago, when I was a programmer, when my boss came along and looked over my shoulder I'd just stop working and gaze around for a while until he bogged off.
He soon learnt not to hassle a genius at work.
 
Many, many, many moons ago, when I was a programmer, when my boss came along and looked over my shoulder I'd just stop working and gaze around for a while until he bogged off.
He soon learnt not to hassle a genius at work.
its the cold shoulder tecnique..
i have had to employ this method of getting people i dont like to
f%*k off on several different occasions
 
i'm not mooning for anybody. my arse is my personal think tank.
 
Many, many, many moons ago, when I was a programmer, when my boss came along and looked over my shoulder I'd just stop working and gaze around for a while until he bogged off.
He soon learnt not to hassle a genius at work.

I can't handle anyone looking over my shoulder either
I also stop,but I don't gaze around,I put the tools down,turn to face them.fold my arms and look them in the eye and wait for battle of the eye contact to conclude
No words,no moaning
 
Many, many, many moons ago, when I was a programmer, when my boss came along and looked over my shoulder I'd just stop working and gaze around for a while until he bogged off.
He soon learnt not to hassle a genius at work.

I used to do that too.

During that hot summer of '76 or thereabouts, I was working as a turner in an engineering company where the boss was always hanging over my shoulder.

This day, he was wearing a sparkling white bri-nylon shirt and I was sick of him standing behind me just off my left shoulder, so I applied a nice heavy cut, selected a nice fast spindle speed and dropped the machine's clutch in and showered him with nice hot swarf.

In less than five seconds his shirt became a string vest.
 
We'll thank you all for your responses. I'm just home from the job and found the fault behind a Class 1 fitting where the connector block neutral had melted onto the back of the casing. Then I had to fix out the stramash in the two way switches. All sorted now and the install buttoned down and tested.

Apologies for for not responding to all your online splaff but I was too busy making money. How do you guys have so much time to chat on this forum?
 
That'll have been 77, when God Save the Queen came out, happy days! :)

Geordie being corrected by Archie,whatever next lol

I agree with Geordie I reckon it was 76 when the miners came out
icon14.png
 
We'll thank you all for your responses. I'm just home from the job and found the fault behind a Class 1 fitting where the connector block neutral had melted onto the back of the casing. Then I had to fix out the stramash in the two way switches. All sorted now and the install buttoned down and tested.

Apologies for for not responding to all your online splaff but I was too busy making money. How do you guys have so much time to chat on this forum?

Some of us are Gentlemen of leisure and some are retired old gits.
 
Geordie being corrected by Archie,whatever next lol

I agree with Geordie I reckon it was 76 when the miners came out
icon14.png

Aye well ... I'm still not sure of the year bt it doesn't matter.

It was a stinking hot summer though, and my mate and I worked directly under a glass skylight and the heat was unbearable.

My mate found a bucket of white paint and some brushes one morning so he and I went up on the roof to paint the skylight over. We spent all day up there !!
 
but fit enough to drive a MR2 from nottingham. hmmmmm.
 
Geordie being corrected by Archie,whatever next lol

I agree with Geordie I reckon it was 76 when the miners came out
icon14.png


if i rem. correct it was '73. joe gormley was trheir leader then.
 
if i rem. correct it was '73. joe gormley was trheir leader then.

Aye .. that was '73 when they socked it to Ted Heath and that's why Thatcher had to have her revenge in '84.

That really hot summer was '76 or '77 though.



In '73 I was working at another place and because of the Miners' Strike, everywhere was working the 3 day week and we were supposed to as well, but the boss said we had our own generator and we did too. It was a little thing powered by a Lister diesel like what drives a builder's cement mixer.

The boss had this little genny parked outside at the reception door and there was a bit of flex from the genny threaded through the letter box and attached to a lamp holder in the reception area. The lamp holder had a 40 watt lamp / bulb in it which flickered dimly.

The rest of the factory carried on regardless because we were on the same feeder as the hospital up the road, so unlike other factories the supply was never switched off.

Anyone passing would hear the putt putt of the genny and see the dim light flickering an leave us alone.
 
Last edited by a moderator:
if i can recall, at the time, a coal face worker earned 4 times as much as a qualified spark. seems not much has changed. but now it's plumbers.
 

Reply to RCD tripping on lighting circuit when lamps (bulbs) are put into light fittings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
667
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
I have a street light circuit on land I rent out. I need to replace 2 of the bulbs. 1 of them is an old Philips 55W SOX Plus, the other is a...
Replies
3
Views
568
Hi all. Removed an ancient light fitting, replaced with a newer one, the light comes on but can't be turned off with the switch. It was working...
Replies
23
Views
844
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock