i was just wondering if anyone could help answer 2 questions for me
1, how many questions need to be correct in the 17th edition update (30 question) exam
and
2, I am struggling to find the answer to this question in the regs
the maximum measured value for BS EN 60898 16A B type circuit breaker is
a) 2.3 ohms
b)2.87 ohms
c)1.44 ohms
d)2.19 ohms
i have been finding it as b - 2.87 but i have been told the answer is actuallly a - 2.3 but i cannot seem to find this number anywhere in the book. Im i just daft/blind/stupid ???
any help would be sooo much appreciated
Probably a typing error your answer is correct 2.87 page 49 BRB table 41.3
18 out of 30
Chris
Upvote 0
BS 7671 value will be 2.87ohms.
On Site Guide value will be the temperature corrected value of 2.87 - 20% = 2.3ohms.
Go with the BS 7671 value.
Upvote 0
Correct me if I am wrong but they are asking for the max measured value (with test meter) which would be 2.3 ohms
ie. 80% of 2.87 to allow for rise in conductor temp under real fault conditions
Upvote 0
Think you may be right....Note to Self, must read posts more carefully in future.:o:D
City and Guilds love wording questions like this to try and catch you out. Rotters!!!!:mad:
Upvote 0
Cheers Lenny.
Ursheee, Lenny is right about C&G's wording of questions. Read them carefully. They love to catch you out:(.
Upvote 0
silly question? but why only 30 questions for 17th?
my C&G 2382 17th edit. was 60 questions? bit confussed:confused:
Upvote 0
If you have never taken the exam before you get 60 questions if you have the 16th edition you get only 30 questions to upgrade.
Chris
Upvote 0
17th edition help please
ursheeee,
acat,
Electrical Courses