Throw this out there what code would you put down on a EICR report where "There is no Main Earth to the installation??
Discuss EICR Code for no main earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Throw this out there what code would you put down on a EICR report where "There is no Main Earth to the installation??
Yep I had day with field engineer as a QS and his words exactly only C2 however.... page 118 NICEIC Inspect and test says it is a C1 ??? contradiction again I ask my lord...
Induced voltages of up to 85?! Really?
Capacitively coupled phantom voltage maybe, but not induced.
Capacative coupling is the most common form of phantom voltages in conductors and they can be picked up using high impedance digital multimeters. A low impedance analogue multimeter will confirm the presence of a phantom voltage as they will not register a result.
is this some sort of homework?Throw this out there what code would you put down on a EICR report where "There is no Main Earth to the installation??
dangerous under fault conditions.Yes C2 because C1 is for immediate dangers, where there is no earth it's only a C2 as its 'potentially dangerous'.
Esc do a good best practice guide. This is, i think, an example of a definite C2. Also waterpipe used as ME is a c2 too.
make notes as required....nothing more...nothing less..C2 and absolutely go to town on it in the Summary and Observations. If it were me, I think I'd do some sort of covering letter or note to the person ordering the report.
Yep ditto the above. Quite often find induced voltages of that size.. Nowhere to go without the main bond..!
what do you think the observations box is for Nick?C2 and absolutely go to town on it in the Summary and Observations. If it were me, I think I'd do some sort of covering letter or note to the person ordering the report.
wellYep I had day with field engineer as a QS and his words exactly only C2 however.... page 118 NICEIC Inspect and test says it is a C1 ??? contradiction again I ask my lord...
what do you think the observations box is for Nick?
That's why you go through the report with them and explain it to them isn't it?
ever heard of a danger notice Nick?Often they're wary and think you're just looking for work. A missing earth conductor I would want them to know I'm not messing. GN3 p.108 para.8 says an unrectified C1 should be notified urgently in writing; in the same vein I'd consider taking the personal decision to extend that to an extremely serious C2. Nothing says I can't, and it is difficult to prove a conversation took place. Something awful could easily happen with a missing earth conductor. It might be useful to be able to demonstrate later you took every reasonable step to draw their attention to the seriousness of the potential danger. Courts don't look favourably on important stuff buried in detail. I'm just risk averse; I can see why I'd do it. If you can't see why you'd do it, don't.
what for?Im the first person (if i can) to jump all over over zealous coding but id be putting a C1 for this regardless of needing more faults or anything, if my house had no MEC id being strolling to the garage to get some 16mm to fit one straight away without considering anything else and my coding would reflect this.
Im the first person (if i can) to jump all over over zealous coding but id be putting a C1 for this regardless of needing more faults or anything, if my house had no MEC id being strolling to the garage to get some 16mm to fit one straight away without considering anything else and my coding would reflect this.
againhahaha, now now play nice i havnt started questioning your abilities have I.
black and white? whos black and white?
can you explain how I can code something different to you can invalidate the report?
I believe the MEC should be installed as a matter upmost urgency end of, i feel a C1 best describes this. you can disagree with that all you want.
course it isIt's a C2 all day everyday no if's no but's you cant change the codes to suit your own personal thoughts, otherwise it would be chaos out there, oh hang on a minute it already is
I saw an eicr that gave a C2 for t&e cables that were in a chase with no capping/conduit, claiming 'no mechanical protection'. Wtf is the sheath dimlo ?!?!
yeah well they probably had it in their minds that pvc/metal channels are `mechanical protection`...lolHaha no. It was rough, chased out brickwork, no filling. But clipped.
Rough but fine basically
If the installation with no earthing conductor also contained a circuit with high protective conductor currents would that warrant a C1?
i did think this forum was grown up for a while. same old same old.