Throw this out there what code would you put down on a EICR report where "There is no Main Earth to the installation??

If you mean the Main Earth Conductor? I found one missing on a Periodic once at a Pharmacy in Bradford, so I just fitted one and moved on. I was on wages at the time! :)
 
Yep I had day with field engineer as a QS and his words exactly only C2 however.... page 118 NICEIC Inspect and test says it is a C1 ??? contradiction again I ask my lord...
 
Yep I had day with field engineer as a QS and his words exactly only C2 however.... page 118 NICEIC Inspect and test says it is a C1 ??? contradiction again I ask my lord...

It is not an immediate Danger, it would take a second fault (L to E) to become so, hence a C2 potentially dangerous, Niccy don't write the rules they just like to think they do.
 
i'd agree with a C2 as it would require a fault ( live part to exposed part ) to present a danger.
 
It all depends on the circumstances No main earth not a good one most situations it would be a C2 i have come across a similar situation where there was an induced voltage of 85 volts in that scenario i would give it a C1
 
Another way of looking at it...is that it is a very high impedance voltage source.
So the reading depends on the input impedance of the test voltmeter.
Also, why it it doesn't present a shock hazard.
 
C2 and absolutely go to town on it in the Summary and Observations. If it were me, I think I'd do some sort of covering letter or note to the person ordering the report.
 
You can't induce meaningful voltages into a conductor without a large number of turns in a coil and a fast rate of change in magnetic flux. Capacative coupling is the most common form of phantom voltages in conductors and they can be picked up using high impedance digital multimeters. A low impedance analogue multimeter will confirm the presence of a phantom voltage as they will not register a result.

Capacative coupling works in the same way a capacitor works, with the insulation between conductors acting as a dialectric.

A phantom voltage picked up by a digital multimeter is harmless.
 
Capacative coupling is the most common form of phantom voltages in conductors and they can be picked up using high impedance digital multimeters. A low impedance analogue multimeter will confirm the presence of a phantom voltage as they will not register a result.

Or a suitable highish-but-not-too-high load added between your digital meter probes achieves the same effect, i.e. a load path causing the capacitance to discharge and the phantom voltage to collapse. Someone said Fluke used to sell one.
 
Throw this out there what code would you put down on a EICR report where "There is no Main Earth to the installation??
is this some sort of homework?

caus if it aint...and your coming in here to ask what is really an open & shut scenario...like what code to be alotting this...then do you really think you should be carrying out ECRs?
 
what do you think the observations box is for Nick?

I think it's for being buried in a long, detailed form full of small print, numbers and technical detail which will have made the average non-technical reader think it's indecipherable and not meant to be read by them and give up somewhere around the top of page 2.
 
That's why you go through the report with them and explain it to them isn't it?


Often they're wary and think you're just looking for work. A missing earth conductor I would want them to know I'm not messing. GN3 p.108 para.8 says an unrectified C1 should be notified urgently in writing; in the same vein I'd consider taking the personal decision to extend that to an extremely serious C2. Nothing says I can't, and it is difficult to prove a conversation took place. Something awful could easily happen with a missing earth conductor. It might be useful to be able to demonstrate later you took every reasonable step to draw their attention to the seriousness of the potential danger. Courts don't look favourably on important stuff buried in detail. I'm just risk averse; I can see why I'd do it. If you can't see why you'd do it, don't.
 
Often they're wary and think you're just looking for work. A missing earth conductor I would want them to know I'm not messing. GN3 p.108 para.8 says an unrectified C1 should be notified urgently in writing; in the same vein I'd consider taking the personal decision to extend that to an extremely serious C2. Nothing says I can't, and it is difficult to prove a conversation took place. Something awful could easily happen with a missing earth conductor. It might be useful to be able to demonstrate later you took every reasonable step to draw their attention to the seriousness of the potential danger. Courts don't look favourably on important stuff buried in detail. I'm just risk averse; I can see why I'd do it. If you can't see why you'd do it, don't.
ever heard of a danger notice Nick?

clearly not...
 
Im the first person (if i can) to jump all over over zealous coding but id be putting a C1 for this regardless of needing more faults or anything, if my house had no MEC id being strolling to the garage to get some 16mm to fit one straight away without considering anything else and my coding would reflect this.
 
Im the first person (if i can) to jump all over over zealous coding but id be putting a C1 for this regardless of needing more faults or anything, if my house had no MEC id being strolling to the garage to get some 16mm to fit one straight away without considering anything else and my coding would reflect this.
what for?

its a 2....
 
Im the first person (if i can) to jump all over over zealous coding but id be putting a C1 for this regardless of needing more faults or anything, if my house had no MEC id being strolling to the garage to get some 16mm to fit one straight away without considering anything else and my coding would reflect this.

Then you'd be wrong. You'd devalue the meaning of a real C1.

This is black and white coding. Anything other than a C2 would be ridiculous and potentially invalidate a report.

You're not one of these 'C1 no RCD protection in bathrooms' types are you?
 
hahaha, now now play nice i havnt started questioning your abilities have I.

black and white? whos black and white?

can you explain how I can code something different to you can invalidate the report?

I believe the MEC should be installed as a matter upmost urgency end of, i feel a C1 best describes this. you can disagree with that all you want.
 
It's a C2 all day everyday no if's no but's you cant change the codes to suit your own personal thoughts, otherwise it would be chaos out there, oh hang on a minute it already is
 
hahaha, now now play nice i havnt started questioning your abilities have I.

black and white? whos black and white?

can you explain how I can code something different to you can invalidate the report?

I believe the MEC should be installed as a matter upmost urgency end of, i feel a C1 best describes this. you can disagree with that all you want.
again


ITS NOT A BLOODY 1...is it.

a 1 is immediately dangerous...is it not

so no main earthing is not immediately dangerous...is it.....(such as exposed live parts)

but under fault conditions?....

and dangerous under fault conditions is a 2...is it not?

think thats cleared this one up...
 
never ceases to amaze me the amount of folk out there that can`t get their heads around the coding system for what are open and shut cases....

i bet their ECRs are full of 1s n 2s for stuff that they have no business failing....

lol....lol..
 
What..........if it's under fault condition, ie enhancing other C1's ? Just thinking ! Short to earth..no earth!!
 
I saw an eicr that gave a C2 for t&e cables that were in a chase with no capping/conduit, claiming 'no mechanical protection'. Wtf is the sheath dimlo ?!?!
 
I saw an eicr that gave a C2 for t&e cables that were in a chase with no capping/conduit, claiming 'no mechanical protection'. Wtf is the sheath dimlo ?!?!

They must have gone a bit deep into that report......taking the plaster off to check ;)
 
Haha no. It was rough, chased out brickwork, no filling. But clipped.

Rough but fine basically
yeah well they probably had it in their minds that pvc/metal channels are `mechanical protection`...lol

this is typical Electrical Trainee stuff is this....i know caus i`v heard folk who i know are Electrical Trainee spouting it in the wholesalers...lol..
 
i did think this forum was grown up for a while. same old same old.

It still is, but you gotta admit, sometimes it is a good idea to run with the herd. Every book ever written on the new coding system would class no main earth as a C2, every electrician worth his salt would class it a C2, the regs class it a C2.... You see where this is going....

It is a C2, no argument. If you want to change the meanings to suit yourself then that's your prerogative, but it makes your reports worthless.

C1 means danger present, C2 means potentially dangerous. If the install is all tickedy boo except for a missing main earth, it is going to be perfectly safe at that moment in time isn't it! So a C2 it is.
 

Reply to EICR Code for no main earth in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
Replies
14
Views
684
So I know why it is done, where it is done and how it’s done, but I’m yet to see a scenario where there is shock danger in a typical bathroom in a...
Replies
32
Views
1K
Hello everyone, I'm wondering if someone could help me with some EICR coding. I am aware that bringing mains tails into a fire rated consumer unit...
Replies
4
Views
460
Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Replies
12
Views
1K
Hi all Done a EICR on a flat which had the link fuse in the service head .. had an earth wire coming off the orange cable to an earth block...
Replies
16
Views
906

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock