I'm looking at Table 7.1(i) in the On Site Guide. Max length of cable runs.

In some cases where there is no RCD protection the length is given as a number with a zs suffix. eg 47zs

The zs suffix means "limitted by Zs" the final circuit line-earth loop impedence.

In these cases is the number part the actual max length? For example 47zs = 47 meters?

Thanks
IMG_20220405_130308.jpg
 
Last edited by a moderator:
Hi

I'm looking at Table 7.1(i) in the On Site Guide. Max length of cable runs.

In some cases where there is no RCD protection the length is given as a number with a zs suffix. eg 47zs

The zs suffix means "limitted by Zs" the final circuit line-earth loop impedence.

In these cases is the number part the actual max length? For example 47zs = 47 meters?



ThanksView attachment 96622

Yes 47 metres max length, - but as this is due to Zs then if the Ze is bigger then normal, then obviously may be much shorter.
 
  • Agree
Reactions: pc1966
The "unlimited" case is voltage drop and you see it has no change between RCD/not and TN-S / TN-C-S

Most other limits are 'zs' for circuit Zs as above, however, there are a few of cases where it lists 'ad' for adiabatic limit being reached (in most cases simply not permitted, and if mentioned at any length then a reason to consider the design in more detail).

Oddly some cases just say 'NP' without a reason (e.g. 20A BS3036 with 2.5 T&E)!
 
The "unlimited" case is voltage drop and you see it has no change between RCD/not and TN-S / TN-C-S

Most other limits are 'zs' for circuit Zs as above, however, there are a few of cases where it lists 'ad' for adiabatic limit being reached (in most cases simply not permitted, and if mentioned at any length then a reason to consider the design in more detail).

Oddly some cases just say 'NP' without a reason (e.g. 20A BS3036 with 2.5 T&E)!
Voltage drop obviously.

I'm sure if I stare at it long enough I'll spot some kind of rational pattern.

Not yet though.

Cheers
 

Attachments

  • IMG_20220405_194105.jpg
    IMG_20220405_194105.jpg
    275.8 KB · Views: 53
  • Funny
Reactions: pc1966

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
iverpool

Thread Information

Title
Max length of cable runs.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
Ray Pooley,
Last reply from
Ray Pooley,
Replies
4
Views
1,752

Advert