I'm looking at Table 7.1(i) in the On Site Guide. Max length of cable runs.

In some cases where there is no RCD protection the length is given as a number with a zs suffix. eg 47zs

The zs suffix means "limitted by Zs" the final circuit line-earth loop impedence.

In these cases is the number part the actual max length? For example 47zs = 47 meters?

Thanks
IMG_20220405_130308.jpg
 
Last edited by a moderator:
Hi

I'm looking at Table 7.1(i) in the On Site Guide. Max length of cable runs.

In some cases where there is no RCD protection the length is given as a number with a zs suffix. eg 47zs

The zs suffix means "limitted by Zs" the final circuit line-earth loop impedence.

In these cases is the number part the actual max length? For example 47zs = 47 meters?



ThanksView attachment 96622

Yes 47 metres max length, - but as this is due to Zs then if the Ze is bigger then normal, then obviously may be much shorter.
 
The "unlimited" case is voltage drop and you see it has no change between RCD/not and TN-S / TN-C-S

Most other limits are 'zs' for circuit Zs as above, however, there are a few of cases where it lists 'ad' for adiabatic limit being reached (in most cases simply not permitted, and if mentioned at any length then a reason to consider the design in more detail).

Oddly some cases just say 'NP' without a reason (e.g. 20A BS3036 with 2.5 T&E)!
 
The "unlimited" case is voltage drop and you see it has no change between RCD/not and TN-S / TN-C-S

Most other limits are 'zs' for circuit Zs as above, however, there are a few of cases where it lists 'ad' for adiabatic limit being reached (in most cases simply not permitted, and if mentioned at any length then a reason to consider the design in more detail).

Oddly some cases just say 'NP' without a reason (e.g. 20A BS3036 with 2.5 T&E)!
Voltage drop obviously.

I'm sure if I stare at it long enough I'll spot some kind of rational pattern.

Not yet though.

Cheers
 

Attachments

  • IMG_20220405_194105.jpg
    275.8 KB · Views: 9

Reply to Max length of cable runs. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
801
Two related questions in 1, if anyone is up for helping! (i) When electricians install supplies, is there anything in the regs that says how many...
Replies
2
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
446
Hi there, I'm Currently doing my design calcs for my college project and doing the actual Zs calculation. Formula is Zs= Ze (or Zdb) + (R1+R2)...
Replies
1
Views
1K
I really hope someone can help me. Last July I got an electricity bill showing an enormous rise in my kwh consumption of about 900% from what it...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock