Discuss Gym treadmill likely load in the UK Electrical Forum area at ElectriciansForums.net

littlespark

-
Esteemed
Arms
Supporter
Patron
Reaction score
17,018
Got an issue with gym equipment. ( I keep telling my wife I’m going to the gym, but she doesn’t believe me!)
The gym owner says the circuit for treadmills trips out every now and again.
I went there last week to find a 16A type C RCBO supplying 1x metal clad double 13A socket.
From here, there was 2 plugs.. each plug run in flex to another 13A double socket fixed to the floor.
One double ran 2 x treadmills… the other ran another treadmill and a stairclimber machine.

The stairclimber comes with what looks like a laptop power supply on an EIC lead.. so I don’t think that’s the problem.

I took out the flex, and extended the radial circuit to the 2 doubles… Just seemed a bit DIY to me.


Trying to find specs on the machines, and it suggests each one is a 9A load… which is going to mean another circuit.
I would assume some diversity as there is little chance all 4 machines will be running full speed at the same time.


The circuit tests ok, and the RCBO ramped at 23mA…. But I’m more inclined to think it’s overcurrent rather than earth fault.


One machine seemed to labour a little as the incline was adjusted… I did recommend he get them serviced.


9F0F6D44-4A64-4162-B970-96789AEB8AE8.jpeg
 
keep out of the gym, i am convinced it does more harm than good!!
 
Yes 9A is realistic as a peak load, because the motors are rated up to 2hp. They are not likely to run at this power for any length of time. They are usually DC motors fed from some kind of speed controller typically PWM from rectified mains. If they don't have active pfc, the power factor might be quite low over much of the output power range.
 
Yes 9A is realistic as a peak load, because the motors are rated up to 2hp. They are not likely to run at this power for any length of time. They are usually DC motors fed from some kind of speed controller typically PWM from rectified mains. If they don't have active pfc, the power factor might be quite low over much of the output power range.

When I looked up the model no. (95T) I get details of 4hp up to 8…. Couldn’t be right for something on a 13A plug.

I don’t think upgrading the OCPD to 20A will make a lot of difference. I might have to suggest a second circuit.
 
When I looked up the model no. (95T) I get details of 4hp up to 8…. Couldn’t be right for something on a 13A plug.

I don’t think upgrading the OCPD to 20A will make a lot of difference. I might have to suggest a second circuit.
Maybe worth putting a clamp meter on the individual machines to check current and leakage.
 
Although its a C curve RCBO, I'll bet it is start up surge that is tripping it. As far as I read it, you have three treadmills and a stairclimber running from one 16A RCBO?
Probably when one or two machines are running, then the start-up surge for another will trip it.

Run a nice, new 4mm 32A radial.
 
Exactly right, Taylor

I didn’t have the specs of the machine last week, but thought a proper radial would be better than the glorified extension leads they were using.

Still don’t have the exact specs, but overload was my first thought.

I’ll try and clamp one of the machines today.
 
Exactly right, Taylor

I didn’t have the specs of the machine last week, but thought a proper radial would be better than the glorified extension leads they were using.

Still don’t have the exact specs, but overload was my first thought.

I’ll try and clamp one of the machines today.
Yes, but the clamp probably wont tell you the surge, only the running current.
 
Yes, but the clamp probably wont tell you the surge, only the running current.
That would depend on what clamp meter you have, some can show the inrush.
Even so, it may show a deviation between machines that are the same and will obviously show the total load, which may help.

The other thing that we are not aware of is has this only started tripping recently or has is it only happening since another machine's been added etc.

It pretty much seems to be a case for a decent supply though.
 
Last edited:
Even the running current, if high enough… knowing a momentary surge would take it past the 16A for long enough…. Or if 3 out of 4 machines running would be too much anyway.

One of them made a different noise when the incline was adjusted… so it may be straining the motor.
I did suggest to unplug this particular machine, see if it helps until I can be there to test them properly.
 

Reply to Gym treadmill likely load in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, just helping someone out and apologies for the long winded post. Would like install a couple of weatherproof double sockets on the patio. 1...
Replies
3
Views
740
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi, Just been scratching my head about this one and wonder if I've missed anything. A few weeks ago I installed a new circuit for a 3kw oven and...
Replies
6
Views
790
Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock