Insulation test live to earth = 0.7 ohms.
This is a long length of buried swa cable (approx 100m) from mains in to submain.
Test done with live and earth disconected at main and with switch off at sub main.
Question - is this an accurate reading or am I misding something.
Its a big job to replace if I've got this wrong ?
 

Attachments

  • 20240228_091021.jpg
    20240228_091021.jpg
    565.6 KB · Views: 25
I would say that that cable is not suitable and should be replaced or repaired. What is the route? if it is underground is there any sign of excavations on the route?
 
If this is a genuine reading, then the cable is severely damaged, and must be repaired, replaced, or taken out of service.
Why would L+N to earth give any better reading?
Chances are that the cable is damaged at one point, and similar measurements taken at the other end of the cable should give some indication of where.
 
Insulation test live to earth = 0.7 ohms.
I wouldn't expect an Insulation test on a MFT to be able to resolve a fraction of an ohm.
Are you genuinely measuring ohms between L & E, or are the units Megohms for example?
 
Also the CPC should be connected to earth during any IR tests.

Here (if SWA) it is very unlikely to make a difference, but more generally with stuff like T&E you can have a live nicked by a screw/nail and it is leaking to the wall, etc, but not to the CPC that still has the insulation separating them (and from wall, etc).
 
Also is the earth conductor above separate from the armour?
 
I'm sorry, but if someone doesn't know the difference between ohms and megaohms, then they probably shouldn't be using a MFT in the first place.
 
0.70 ohm between live earth you will have a 300A+ flowing.
 
  • Like
Reactions: Pretty Mouth
I would say that that cable is not suitable and should be replaced or repaired. What is the route? if it is underground is there any sign of excavations on the route?
Underground and laid about 20 plus years ago.
 
So is it 0.70 ohms or 0.70 Mohm?
 
very good question and I was just about to aske the exact same question, hopefully the OP will come back and answer it
megaohms 🫣
 
That'll be Meg ohm then😐
I had a college teacher who said mega ohms I cringed every time he said it.
 
  • Funny
  • Like
Reactions: DPG and sidekick
Also the CPC should be connected to earth during any IR tests.

Here (if SWA) it is very unlikely to make a difference, but more generally with stuff like T&E you can have a live nicked by a screw/nail and it is leaking to the wall, etc, but not to the CPC that still has the insulation separating them (and from wall, etc).
2 core swa and armour used as earth
 
Disconnect the line and neutral at both ends to remove any possible external influences switching off can't be guaranteed.
 
  • Like
Reactions: DPG and sidekick
That'll be Meg ohm then😐
I had a college teacher who said mega ohms I cringed every time he said it.
si units.jpg
Hate to say it Westward, but mega Ohm is the correct way of defining it.
 
I should also say that this swa cable has a 63a mcb at the front end and is randomly tripping ?
 
Is that with whatever's at the far end switched off?
No tripping when sub main switched off as that was only briefly while testing .
Live and earth disconnected at front end (neutral still connected) and mains switch and all breakers off at back end to test. Random tripping was when all on (2 to 3 times in last 24 hrs)
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
.
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
If other, please explain
.
Business Name
.

Thread Information

Title
Insulation test L to E long length of SWA
Prefix
N/A
Forum
Electrical Testing & PAT Testing Forum
Start date
Last reply date
Replies
35

Advert

Thread statistics

Created
sidekick,
Last reply from
sidekick,
Replies
35
Views
4,302

Advert