I've fitted this into my new place an old bungalow and it's extracting from the bathroom.

It performs great but the ducting gets full of water, I mean Like loads ! I rwalised when the fan started to make a funny noise.

DO I need a fall on the ducting like you do on a waste pipe ?

I'm guessing I do but I'd never have thought so.

The ducting run is about 8m through the gable wall, there are no soffits on the house for it to vent from as this would be a much shorter wall. The fascia board is hard onto the brick work.

Any experiance of this from you's ?
 
yes, the water is condensation from the warm air hitting the cold ducting in the roof, a slope on the ducting will help, along with replacing the standard ducting with the ducting that comes with insulation all around it, hope this helps.
 
A fall might help. Alternatively a condensate trap and drain fitted within the duct run. If it's running through the loft space, chuck some insulation over the ductwork to help keep the condensation down.

[edit] as already stated above! Must learn to type quicker.....
 

Reply to 100mm Mixed flow extract fan ducting prob in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've just had a look at an extractor fan not working. As per title it's a bungalow and there are no external walls, so it vents through the loft...
Replies
28
Views
3K
Hi. My current axial Xpelair model 92614AW ground floor bathroom extractor fan is installed in zone 1 and doesnt work efficiently at all. Its wall...
Replies
22
Views
2K
So I had a ceiling repair done in my bathroom due to water damage. The neighbors toilet above me was leaking for who knows how long. Mold...
Replies
1
Views
710
Evening all.. I have just been core drilling a 105mm hole for an extractor fan in a bathroom wall. I had a good look around on my pre works visit...
Replies
7
Views
2K
Hi all, I have a 100mm ceiling mounted bathroom extractor to replace. It is ducted to the outside via flexi ducting, which runs in the floor...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock