Discuss 10mm joined to 6mm for exterior charger in the UK Electrical Forum area at ElectriciansForums.net
I have a job where the client wants a 7kw car charger 50 meters away from his house. The problem is there is a 6mm that's been pre wired 10 meters through his house from the main consumer unit to an exterior wall and sealed up. So I would have to use that and join onto the 10mm exterior and put on a 32amp MCB. Can see any issues doing this?
Why 10mm ? Depends on cable run and voltage drop.
Assuming the 6mm is TandE then barring anything too exotic you will be good for a 32/40 amp mcb.
I had a few instances of a ev charger tripping a 32 amp mcb and some manufacturers recommend a 40 amp.
Might be worth checking?
You could look at taking 2 core swa from the existing cable in suitable outdoor box. Keeps costs down, Using armour as cpc in cable run. Dont terminate the armour as the earth at charger as you will use a rod.
It is late and without doing the calculations on voltage drop you might manage to use 4mm 2 core swa depending on install method but 6mm 2 core swa will almost certainly be adequate . Saves using 10mm.
Hi - can I ask what is it you are concerned about? Is it the voltage drop, the ccc change, the cpc size and the earthing system of the installation, the cable installation method and jointing, or ... :)
Voltage drop mate. Just seems illogical way round. I'm running 2 core 10mm to charger exterior and making a tt island at source.
Reply to 10mm joined to 6mm for exterior charger in the UK Electrical Forum area at ElectriciansForums.net
I would like to hide the cable to an EV charger. The consumer unit, meter cabinet and charger would all be on the same wall. About 5 metres from...
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Help please! I need a Tesla Gen 2 EV charger fitted in my garage which is 22m from the consumer unit. My electrician is proposing to route a 6mm...
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...