The saga continues. I was told today by an engineer at Central Networks that it is inverter output that is important when considering the G83 threshold.

Hopefully this will be the stance all DNOs take before long.
 
It is absolutely clear in the G83 document that it must refer to the inverter and it is the inverter - not pv panels - that are G83 type tested.

I'm still waiting for a reply from the ENA on my questions to them - that were written to persuade them to get all DNOs to agree to a consistent set of rules.
 
The saga continues. I was told today by an engineer at Central Networks that it is inverter output that is important when considering the G83 threshold.

Hopefully this will be the stance all DNOs take before long.

Not the amps??? The Fronius 3.6tl has max ac output of 3680 and 16 amps and will take a string of 17 x 235w panels ...
 
Well you can work out the max output in amps if you know the max ac output of the inverter

A customer of ours has had a tripping fault, where by his 16amp mcb has been tripping on peak days. This was caused by the assumption that his ac supply was 240vac (we know what it is meant to be!), but he was at the edge of the network on a fellside. Because he was getting occasional ac volt drop to 230vac or slightly lower this tripped his breaker because the amps had risen over 17amps on peak days!
Food for thought when working in rural areas.
 
A customer of ours has had a tripping fault, where by his 16amp mcb has been tripping on peak days. This was caused by the assumption that his ac supply was 240vac (we know what it is meant to be!), but he was at the edge of the network on a fellside. Because he was getting occasional ac volt drop to 230vac or slightly lower this tripped his breaker because the amps had risen over 17amps on peak days!
Food for thought when working in rural areas.

Could you not install a 20amp mcb? The mcb is just to protect the cable and not limit the output?
 
Could you not install a 20amp mcb? The mcb is just to protect the cable and not limit the output?
The thing is, you will not be limiting the export to 16amp/phase. You know and I know that this does not make much difference, but DNO would probably get upset if found out?If you left as 16amp though it would be a pain with nuisance tripping at peak, possibly system off during customers summer hols abroad?
 
The thing is, you will not be limiting the export to 16amp/phase. You know and I know that this does not make much difference, but DNO would probably get upset if found out?If you left as 16amp though it would be a pain with nuisance tripping at peak, possibly system off during customers summer hols abroad?

The inverter should limit the current under G83, not the MCB!
There's nothing at all wrong with using a 20A MCB if the AC supply to the inverter is 2.5mm2 and above with installation conditions allowing. It's got nothing at all to do with the DNO.
Also, I'm gobsmacked that 17A is tripping a 16A MCB.
 
Last edited by a moderator:
And is the G83 limit 16 amps at the current operating voltage or at 230?

The legislation says:, "...the source of energy does not produce an electrical output exceeding 16 amperes per phase at low voltage;"

So it is defined in Amps in the legislation rather than Watts. That some DNO's produce an interpretation in Watts is just that.... an interpretation.
 

Reply to 16A threshold for G83 - Array size or inverter output? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

I thought I had an understanding of how to size an inverter but I think I have become slightly confused after taking to some proposed installers...
Replies
3
Views
2K
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
TLDR - I have a system that is supposed to have optimisers fitted, but I am not sure they have been fitted. The detail: Back in March I had a...
Replies
11
Views
3K
Hope this all makes as much sense as i can make of it and my "problem" can get sorted via some guru on here... Just a quick background on myself...
Replies
4
Views
1K
Hello All Can I say to start with I am not an electrician but used to be a heating engineer (yes I can hear the groans). I have wired the...
Replies
85
Views
14K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock