Discuss 2.5mm Ring wired off a 4mm Radial in the UK Electrical Forum area at ElectriciansForums.net
Chris
Hi,
I have been testing a domestic property today and when i started to look into the kitchen sockets there is a 4mm radial from the DB going to one socket on one side, the 4mm radial is cut into and JB'd and 2x2.5mm cables run out forming a ring for the other 4 sockets...
Does this obey regs? I know you can run 2.5mm spurs off 4mm but havent seen or heard of this before?
Hi,
A lollipop circuit then, don't like em but don't think they are against the Regs, or so I have heard on this Forum from time to time.
Hi,
One would think if you do what you suggest you would need to reduce the size of the OCPD at or near the change of cable size, wouldn't you????
Are you talking about a 2.5mm spur off a 4mm radial? It is compliant if you only have 1 socket outlet as they are rated 13a so if any higher load was placed on the cable the socket would fail.
Is it simply a case of "get some power in there, 4mm will do it...then get some sockets off that, 2.5 rfc will do?"
I ask this as a complete novice, but I can see some logic in such a lollipop arrangement...
However, I have no clear idea what circuit protection would be appropriate, given I have no idea what the final load might be...
maybe one level at the CU, and another at the junction with the rfc?
Or maybe just assume that the final load will never be enough to cause a fire?
Hmmm...
think I need to get an electrician in!
Whether a 4mm radial, or a 2.5 rfc from source, it would still be generally a 32A OCPD.
I just think it over complicates matters and makes it more confusing for the next spark to work on the circuit.
It shouldn't be done, but its compliant, so hey.
Reply to 2.5mm Ring wired off a 4mm Radial in the UK Electrical Forum area at ElectriciansForums.net
Hello, I need to run a mains spur off the existing ring main in a domestic property. To get the double socket to the correct place I have to drill...
I found a 13A FCU, connected to the kitchen ring supplying an outdoor junction box, providing two SWA 2.5mm radials. Unconventional? yes. One...
Essentially I have a "normal" socket in a ring mains, i.e. one 2.5mm T&E going in and one 2.5mm T&E going out. I am looking to simply add two more...
Im just curious as to peoples thoughts on the following install I seen on a video from an Electrical firm today and they did the following: Ran...
