If it were me I would be condemning the whole thing until a thorough eicr inspection was carried out on the entire installation.

But 99% of landlords I know won’t pay for a proper eicr to be done and will just get bodge it a scarper round to ‘fix’ the problem


I'm waiting on the landlords reply. I have told him I want it investigated and someone registered who can provide a cert for the work
 
So, what power rating are your showers?
 
ABB Switchgear is very good.

All that needs is a 230v coil, n/o contactor rated 40A or above. They come with 4 pole but only use 2. It's suitably protected against overload by the 40A MCB. That has overheated either due to contactor failing or poor termination. Just get the contactor and damaged wiring replaced.
 
It was basically smoking while my son was in the shower. We had to turn it off as nothing tripped

The smoking will have been caused by the overheating of the conductor and the consequential burning of the plastic insulation (most likely due to a poor termination). It's unlikely any of the protective devices would trip because electrically the only fault appears to have been a bad termination, there doesn't appear to have been any unwanted connections say between live and neutral or earth which would cause the devices to trip.

Basically it looks like a simple case of bad workmanship when it was installed, but as I said, definitely not the first time this has happened.

As for you wanting to see paperwork from the electrical contractor (I use the term loosely based on what you've said), you're not the person ordering the work so technically you've got no right to see the paperwork.
 
ABB Switchgear is very good.

All that needs is a 230v coil, n/o contactor rated 40A or above. They come with 4 pole but only use 2. It's suitably protected against overload by the 40A MCB. That has overheated either due to contactor failing or poor termination. Just get the contactor and damaged wiring replaced.

Any reason why the power never cut to it?
 
ABB Switchgear is very good.

All that needs is a 230v coil, n/o contactor rated 40A or above. They come with 4 pole but only use 2. It's suitably protected against overload by the 40A MCB. That has overheated either due to contactor failing or poor termination. Just get the contactor and damaged wiring replaced.

Any reason why the power never cut to it?
The smoking will have been caused by the overheating of the conductor and the consequential burning of the plastic insulation (most likely due to a poor termination). It's unlikely any of the protective devices would trip because electrically the only fault appears to have been a bad termination, there doesn't appear to have been any unwanted connections say between live and neutral or earth which would cause the devices to trip.

Basically it looks like a simple case of bad workmanship when it was installed, but as I said, definitely not the first time this has happened.

As for you wanting to see paperwork from the electrical contractor (I use the term loosely based on what you've said), you're not the person ordering the work so technically you've got no right to see the paperwork.


Thanks for the detailed answer. As for paperwork I really just want to make sure that he doesn't send over someone who has no electrical expertise at all. As he has already done. He sent over someone I knew well and so knew they didnt have the knowledge
 
might be an idea to get your local council H&S involved. if i saw that "in the flesh", I'd condemn the lot.
 
Any reason why the power never cut to it?
Hi - the 40A MCB is designed to not trip at 40A, it's ok with that load. Your 9.5kW shower will draw approx 9500/240 = 40A . So unless both showers went on at once (or some other fault) the MCB will run happily. That contactor is rated at 40A so it should be ok, but it is on its rated max and they do have an operational life limit. From the pics ( :eek: ) I suspect a poor termination has caused the overheating, as per @SparkyChick.
 

Reply to 2 electric showers and melted live wire from relay in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

This from a while ago but reading about everyone elses problems tonight made me remember this one. The original job was the lights in a recent...
Replies
1
Views
1K
Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
Replies
16
Views
2K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
160
Hi, thanks in advance for any advice here please on a safety worry... My son lives in a rented house and recently got a strong electric shock...
Replies
3
Views
2K
Hello, I have just posted in the Electrician's section one photo and two videos of what I believe to be a dangerous situation of short circuits...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock