Discuss 2330 Level 2: Safe isolation in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

M

Mr Curnow

1- To start off we first check the tests leads for damage.
2- Next test between Line and Neutral to see if it's live.
3- Turn off the supply, place the warning sign on the lock, lock it.
4- Keep the key in your pocket.
5- Next test [Line-Earth] [Line-Neutral] [Neutral-Earth].
6- Prove that the tester is still working by using the proving unit.

Is this right? Will I pass by doing this?
 
First off you should as you say check the leads for damage, but you should then check the tester works, either by using the proving unit or a known live supply. This will verify both the tester and the proving unit.
Then you should check for voltage between all conductors, not just Line and Neutral.
Turn off supply and re-test between all conductors, before placing warning notice and locking off and placing key in pocket. Not much point locking off, if the MCB hasn't isolated the supply.
Re-test tester with proving unit, or known live supply. Again not much point in locking off, if your tester or proving unit has packed up.
Then place warning etc.
If you have to go away from the board for any reason to conduct any tests, such as to prove the item you are working on is isolated, or to find a known live supply then place warning etc. before you go.
 
First off you should as you say check the leads for damage, but you should then check the tester works, either by using the proving unit or a known live supply. This will verify both the tester and the proving unit.
Then you should check for voltage between all conductors, not just Line and Neutral.
Turn off supply and re-test between all conductors, before placing warning notice and locking off and placing key in pocket. Not much point locking off, if the MCB hasn't isolated the supply.
Re-test tester with proving unit, or known live supply. Again not much point in locking off, if your tester or proving unit has packed up.
Then place warning etc.
If you have to go away from the board for any reason to conduct any tests, such as to prove the item you are working on is isolated, or to find a known live supply then place warning etc. before you go.

I think they want you to lock it off anyway, If I didn't lock it off then I would fail the exam, It's not as same as it would be on site. Exams are over protective, well you have to be with electricity.
 
Wouldn't checking between all conductors trip it out though, say if you test from line to earth then the MCB will cut the circuit because current is flowing to the main earthing terminal. I think it's called earth fault current.
 
This is the procedure I write in any college exams. Hope this helps.

- Check with customer whether it's ok to isolate
- Disconnect all loads
- Locate source of supply and isolate
- Lock off and place warning signs
- Select and test GS38 voltage indicator on proving unit
- Test supply is isolated
- Retest voltage indicator on proving unit
- Start work if all of the above has been followed and installation is proved isolated
 
-Check which circuit is to be isolated
-Check if it is ok to isolated said circuit
-Lock off label leave yourself safe <<lollys PLACE KEY IN POCKET!!!!!!!!!!!
-test voltage indicator on proving unit or known supply
-test l-n l-cpc n-cpc
-test voltage indicator on proving unit
-Assess if there are any more precautions you could put in place
-Start work
 

Reply to 2330 Level 2: Safe isolation in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
659
Hi I am looking for advice please. Last week I done my am2. And the only thing I failed on was safe isolation of the 3 phase circuit. The...
Replies
11
Views
5K
I had Scottish Power moving a supply this morning from one building to another so an extension could be built. I had everything ready for them...
Replies
1
Views
780
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
769

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock