Hi all: Not got Regs book here & can't for the life of me remember the max length of Run for 25mm tails installed in trunking to feed a CU.
 
If you need longer than 3M from the service head, install a switch fuse. The limit is the DNO suggesting that their fuse will only protect up to 3M.
 
Cheers guys: The old age is getting to me lol, damned if I could remember. It was a question I was asked by someone who wanted to do a 15m run of tails from the Head to a CU.
Appreciate the answers.
 
Pretty sure its not in the IEE regs, its a supply authority regulation.

Try 433.2 and 434.2. In both cases 3m is given as the maximum allowable length downstream of the service fuse. However some DNOs specify 2m as a maximum length.
 
  • Like
Reactions: 1 person
top,
they are not "actually" double insulated.
They are technically insulated & sheathed.
The "grey" covering on T&E & tails is not classed by the cable standards, nor the cable makers as insulation!
 
  • Like
Reactions: 5 people
top,
they are not "actually" double insulated.
They are technically insulated & sheathed.
The "grey" covering on T&E & tails is not classed by the cable standards, nor the cable makers as insulation!
You are of course correct. I stand corrected Sir. ;)
 
Have had Dno before refusing to fit new meter until the 1m tails (insulated and sheathed) were all boxed in. Told him it was nonsense... Maybe he had a point.
 
top,
they are not "actually" double insulated.
They are technically insulated & sheathed.
The "grey" covering on T&E & tails is not classed by the cable standards, nor the cable makers as insulation!

Proper ----!!! I think you and I could become very good friends :D
 
  • Like
Reactions: 1 person
top,
they are not "actually" double insulated.
They are technically insulated & sheathed.
The "grey" covering on T&E & tails is not classed by the cable standards, nor the cable makers as insulation!

buy the same argument, T/E is not double insulated either. it is also insulated and sheathed.
 
cakey were the tails going into the meter boxed in ??? and what is the length if not in trunking please ??
 
I prefer when possible not to box in or cover up meter tails. I would rather DIY Charlie knows where they are so he doesnt go drilling holes in things and doing himself or others some serious damage.

Cheers.......Howard
 
  • Like
Reactions: 1 person
cakey were the tails going into the meter boxed in ??? and what is the length if not in trunking please ??

Tails going to meter were just over 2m from rifle board with the first 1.5m ish boxed in trunking. He wasn't happy till every bit was completely boxed in.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
25mm Tails in Trunking
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
17

Thread Tags

Advert

Thread statistics

Created
Specialist,
Last reply from
cakey,
Replies
17
Views
5,947

Advert