testing an installation(that we have just finished) where the client want to choose a few circuits and check it against the test sheets, Now the circuits are 3- 240mm single core cables in parrallel (24 in total in a data centre) I have tested r1+r2 with 3 different fluke multi function testers that have been callibrated and i get different readings every time,as in 1 tester will give me 2 or 3 different readings on the same circuit , the next 2 or 3 completely different readings and so on,changed batteries, swaped leads, but nothing seems constant, doing my head in,one told me a 6m run had more resistance(0.05 no way) than a 70m run(0.01), only thing i can think of is Edmunsons can't callibrate properly and are ripping us of, think readings should all be about 0.00 -0.01 but getting -0.03 to 0.18( different every time)
 
hi
ye, same problem with my 1653 from new. never the same reading twice..... wont get another one!

regards
gary
 
You're trying to measure quite low values at the limit of the range/resolution of the instruments so any errors from probe contact etc. will appear to be amplified.

+/- 0.2 ohms I wouldn't really lose any sleep over.
 
Thanks for that, Fluke does seem a bit random compared to the meggers we used to use, is there a meter that can measure resistance in micro ohms?
 
Most people get there meters checked but never their leads, I get through loads of leads as they get abused all the time.
 
  • Like
Reactions: 1 person
As Archy hinted you are expecting precision beyond the capability of your Fluke MFTs. If you wish to measure such values with greater precision you require a special type of micro-ohmeter called a Ductor. Probably best to hire one if you do not have a regular requirement as they are expensive pieces of kit.
 
As Archy hinted you are expecting precision beyond the capability of your Fluke MFTs. If you wish to measure such values with greater precision you require a special type of micro-ohmeter called a Ductor. Probably best to hire one if you do not have a regular requirement as they are expensive pieces of kit.

You also need to know how to use a Ductor tester too, ...ie, test kit settings and testing position of current and potential spikes.... You'll also have to substantially bridge the cables at one end under test, as you don't use wander leads with this kit!! lol!!
 
ive tested for over 6 years with various meters and never come across a high Ze on a TNC-S. Now i've got this fluke 1652C ive found two seperate installations with the tnc-s Ze over 0.68!!!. is it the meter or just a coincidence???
 
ive tested for over 6 years with various meters and never come across a high Ze on a TNC-S. Now i've got this fluke 1652C ive found two seperate installations with the tnc-s Ze over 0.68!!!. is it the meter or just a coincidence???

How are you nulling the leads ?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
3 Fluke testers, different results?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
12

Advert

Thread statistics

Created
doogle,
Last reply from
needasparks,
Replies
12
Views
3,202

Advert