yes, but cable could also be SWA with the armour earthed but not used as cpc. the cpc core is the same size as the L and N.
Or flex, or hituff or ......,
Discuss 0.00 ohms r1+r2 on radial circuit? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
yes, but cable could also be SWA with the armour earthed but not used as cpc. the cpc core is the same size as the L and N.
Slight hypocrite to note the importance of a capital letter when needed ....lol telectrixno. with a rfc, you measure end/end of each conductor. these values are denoted by lower case r. when you cross connect on a RFC, or just connect L-E on a radial, you then measure R1+R2. ( denoted by upper case R ).
Slight hypocrite to note the importance of a capital letter when needed ....lol telectrix
Although I cannot say anything either ... but I didn't bring the subject up :laugh3:
Reply to 0.00 ohms r1+r2 on radial circuit? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net